Correct. With an integrated power supply, the primary side may be Class I and the secondary may be SELV. But that would make the whole housing Class I and needing earthing.If you Earth something then it sure as hell isn't SELV. (The whole point of SELV is that it is separated from Earth.)
BUT BUT, the whole may have been constructed as a double insulated assembly.
Isf this is the case, there should be a double insulated logo on the thing.
@Anders does it have this symbol on it?
Please provide a photo of teh light's label, or maybe tell us what the installation instructions say......