Discuss Earthing SWA in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
52
As an adult learner, I have lots of theory but not enough practical experience so I'm hoping I can get some help here (not abuse). I'm trying to get my head round earthing SWA to an outbuilding with no extraneous conductive parts. I understand the problems of exporting a PME supply etc. If I have a 3 core 6mm2 SWA and use one of the cores as the CPC and the house CU has RCD protection why do I need to earth the SWA? My thinking (probably wrong) is that if a spade goes through the cable it will cause a short between phase conductor and earth conductor and trip the RCD?
 
If the armour is not earthed, and your spade happens to dig into the armour and the live (L, line) only, ... the armour goes live, so does your spade, ... and anyone touching the metal parts.
 
If the armour is not earthed, and your spade happens to dig into the armour and the live (L, line) only, ... the armour goes live, so does your spade, ... and anyone touching the metal parts.
Thanks for taking the time to reply. Makes perfect sense - why didn't I figure that out!
 
  • Like
Reactions: DPG

Reply to Earthing SWA in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
447
resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
Replies
1
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock