- Reaction score
- 25,562
You do not base findings in an EICR predicting the actions of a child. Your findings are based upon BS7671 which does not differentiate between a child and an adult.
Discuss EICR and RCD's. Is it a C2 or C3? in the UK Electrical Forum area at ElectriciansForums.net
Supplementary bonding does not remove the requirement for RCD protection of bathroom circuits. 30mA RCD protection of bathroom circuits may well remove the requirement for supplementary bonding though.According to the tick sheet there is supplementary bonding in the bathroom so no rcd required there. There is also IR values in L-N column, so everything got disconnected, all lamps removed etc to preform this test - I don't think so.
I would complain to NAPIT as the standard of the report is poor with unwarranted C2s.
All said though a board upgrade is a good recommend.
The tick sheet says there is RCD protection for the bathroom circuits.Supplementary bonding does not remove the requirement for RCD protection of bathroom circuits. 30mA RCD protection of bathroom circuits may well remove the requirement for supplementary bonding though.
Q1 it says u have 10 mmm main tails these are usually 25 or 16 minThe tick sheet says there is RCD protection for the bathroom circuits.
Please read my last post send that report to Napit and ask for their opinion,, if u can post response on here thanksThank you all and everyone for their comments.
I won't comment whether I am a 'greedy landlord', I certainly
don't wish to be taken advantage off. Equally I don't think I take advantage of others.
Re-capping:-
1) 2nd Floor flat in a block built NEW in 1997.
2) Five years ago I have a satisfactory EICR.
3) Now I have a C2 (Potentially Dangerous). This rating can be changed as I have a quotation to "fit a new fuseboard to meet current regulation" - as written by the electrician. A new fuseboard solves my problem?
Logic question - Why is it a C2 if RCD's are NOT mandatory given it was satisfactory five years ago? Why wasn't it a C2 five years ago?
Thanks everyone again.
I got That Bible Lol..
How funny I've just been having this discussion with my knowledgeable supplier as I have to do and EICR on a 7 way wylex board with no RCD and he said as I can't prove that the cables are deeper than 50mm and the customer does not want to a new board then he suggested an up front RCD.It's not compliant with section 314. That's not up for debate at all.
Lighting circuits can have RCD protection added at any point on them to facilitate alterations.
How funny I've just been having this discussion with my knowledgeable supplier as I have to do and EICR on a 7 way wylex board with no RCD and he said as I can't prove that the cables are deeper than 50mm and the customer does not want to a new board then he suggested an up front RCD.
I've just read section 314 and I interpreted it to mean every circuit must be RCd protected not a batch of circuits I.E like the 5 and 5 way boards.
can you point out please how I'm reading it wrong
Thanks
How funny I've just been having this discussion with my knowledgeable supplier as I have to do and EICR on a 7 way wylex board with no RCD and he said as I can't prove that the cables are deeper than 50mm and the customer does not want to a new board then he suggested an up front RCD.
I've just read section 314 and I interpreted it to mean every circuit must be RCd protected not a batch of circuits I.E like the 5 and 5 way boards.
can you point out please how I'm reading it wrong
Thanks
Thanks for you reply but can you answer my other question which was if the RCD should not trip other circuits then how come we fit split load boards?Selectivity.
upfront rcd trips, everything goes off.
your knowledgable supplier is well out of date.
As is this thread.
Very true but we are often accused of stitching the customer up so knowing its an old board with no RCD fitted and if we are saying that its a fail with no RCD, then I'm trying to give him options other than a new board if that's possible.Surely if its an EICR you don't need to provide an rcd unless the client has asked??
Sorry my fault i Jumped in on an old thread and started to ask questions about fitting an upfront RCD, whereas it might have been better to start a new threadAs this has been brought tot the top of the forum and I haven’t seen it... why has no one picked up the high r2 reading on circuit 2.
That report is awful, the form layout is also awful.
Mark it unsatisfactory. Then personally I would say a new board would be the best course of action if he declines at least you've done what you were paid to do and no one can argue with you on thatThanks for you reply but can you answer my other question which was if the RCD should not trip other circuits then how come we fit split load boards?
confussed
[automerge]1593442977[/automerge]
Very true but we are often accused of stitching the customer up so knowing its an old board with no RCD fitted and if we are saying that its a fail with no RCD, then I'm trying to give him options other than a new board if that's possible.
From the OSG:if the RCD should not trip other circuits then how come we fit split load boards?
I thought his name was "Deleted Member" as some sort of joke???I'm just trying to work out who the deleted member is who was giving all the dislikes at the beginning .
Exactly what i was thinking!If there was no supplementary bonding in the bathroom or RCD protection to the circuits that warrants a C2
Some of our tenants have the mem boards fitted in 2005 or before . Ones where some is rcd protected other half isnt. When doing eicrs its a c3 that cables less than 50mm are not rcd protected and also c3 that lights arent rcd protected.
If however we want to do work on these circuits we either swap the mcb for an rcbo or move the mcb over to the rcd side.
As for an upfront rcd not being compliant...so you have a client with an old cartridge fuse board asking you to put an extra light on the circuit...not that big a job...you're going to honestly turn to them and say
Yeh well first im going to have to test the whole install as i have to change the whole board.
As i suspect dave from the pub would soon happily be used instead
[/QUOTE
I use an rcd fcu
I do that too. Did a job for a friend who wanted an extra socket put in did an rcd fcu so everything I put in was protected by a 30ma rcdExactly what i was thinking!
[automerge]1593541730[/automerge]
Hi been using the Napit Code breaker for a few year now and if I see none or a lack of RCD protection for circuits not clipped direct or in trunking or conduit its a straight C2No it’s not correct.
There is no requirement to install RCDs in Consumer Units.
There are requirements to protect some circuits, which would require an RCD be placed in or very close to the Consumer Unit.
However, the person who conducted the Inspection should be listing the instances where RCD protection is required but not been provided, and then applying a code for each of those instances.
In many instances, RCD protection can be provided, simply by the installation of an RCD or RCBO in or close to the Consumer Unit.
Only thing that’s changed, is the person who conducted the latest inspection, wants to make money from you.
This is at odds with Best Practice Guide 4, which codes it as C3Hi been using the Napit Code breaker for a few year now and if I see none or a lack of RCD protection for circuits not clipped direct or in trunking or conduit its a straight C2
just on the grounds of section 5.12.3, 522.6.202, no protection of cables in wall less than 50mm from surface, which can not always see but can assume if the wall is a standard 100mm wall, that it does not conform, we sparkies are not looking to rip people off as Ive seen peeps on here giving good sparks a bad name on for telling folks you got to spend money on your property to get it to a good and safe standard etc. as introducing RCD's or RCBO's also detects any Earth to Neutral defects if not already identified on the EICR
this is just my opinion and my clients will have a chose to do it or not.
Regards Jelade Electrical Services
Yet Napit , Niceic and others sit on the electric safety first committee that write up these best practices guides and are supposed to come to a mutual agreement , yet Napit C2 this in their own guide book? Bizarre!This is at odds with Best Practice Guide 4, which codes it as C3
The date it was designed has absolutely nothing to do with how safe or dangerous it is.Hi Everyone.
I have done an EICR at a cleaning company today. The installation is less than a year old as they have had a refurb. The spark who did was retired and wouldn't issue any certification! In fairness the job is to an ok standard but there isn't any RCD protection on anything. Am i correct in thinking that because it was 'designed' under 7671:2018 that it is a C2? or would C3 still cover it?