Discuss EICR Code for no main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Throw this out there what code would you put down on a EICR report where "There is no Main Earth to the installation??

If you mean the Main Earth Conductor? I found one missing on a Periodic once at a Pharmacy in Bradford, so I just fitted one and moved on. I was on wages at the time! :)
 
Yep I had day with field engineer as a QS and his words exactly only C2 however.... page 118 NICEIC Inspect and test says it is a C1 ??? contradiction again I ask my lord...
 
Yep I had day with field engineer as a QS and his words exactly only C2 however.... page 118 NICEIC Inspect and test says it is a C1 ??? contradiction again I ask my lord...

It is not an immediate Danger, it would take a second fault (L to E) to become so, hence a C2 potentially dangerous, Niccy don't write the rules they just like to think they do.
 
i'd agree with a C2 as it would require a fault ( live part to exposed part ) to present a danger.
 
It all depends on the circumstances No main earth not a good one most situations it would be a C2 i have come across a similar situation where there was an induced voltage of 85 volts in that scenario i would give it a C1
 
Another way of looking at it...is that it is a very high impedance voltage source.
So the reading depends on the input impedance of the test voltmeter.
Also, why it it doesn't present a shock hazard.
 
C2 and absolutely go to town on it in the Summary and Observations. If it were me, I think I'd do some sort of covering letter or note to the person ordering the report.
 
You can't induce meaningful voltages into a conductor without a large number of turns in a coil and a fast rate of change in magnetic flux. Capacative coupling is the most common form of phantom voltages in conductors and they can be picked up using high impedance digital multimeters. A low impedance analogue multimeter will confirm the presence of a phantom voltage as they will not register a result.

Capacative coupling works in the same way a capacitor works, with the insulation between conductors acting as a dialectric.

A phantom voltage picked up by a digital multimeter is harmless.
 
Capacative coupling is the most common form of phantom voltages in conductors and they can be picked up using high impedance digital multimeters. A low impedance analogue multimeter will confirm the presence of a phantom voltage as they will not register a result.

Or a suitable highish-but-not-too-high load added between your digital meter probes achieves the same effect, i.e. a load path causing the capacitance to discharge and the phantom voltage to collapse. Someone said Fluke used to sell one.
 
Throw this out there what code would you put down on a EICR report where "There is no Main Earth to the installation??
is this some sort of homework?

caus if it aint...and your coming in here to ask what is really an open & shut scenario...like what code to be alotting this...then do you really think you should be carrying out ECRs?
 

Reply to EICR Code for no main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
598
So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a...
Replies
8
Views
236
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
414
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Hi, Ignoring the appauling conductor terminations which I found, in the background of the photo you can see a really odd neutral tail terminated...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock