Discuss EICR code in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
18
I'm doing a EICR on a caravan site. Came across 5 circuits each supplying about 13 16A socket outlets. All are protected by 63 A mcbs and all wired in 6mm twin armoured cable buried underground. The cable rating for the cable is 46A with the ref installed etc.

Im undecided if I should code 3 this as the installation has been in service for over 30 years and cable shows no signs of thermal damage etc. Or if I should put my foot down, code 2 it and go from there.

Any advice would be much appreciated
 
IMO the 16A sockets can not be protected by 63A MCB as they are rated at 16A. They need 16A protection.

The cable needs coding as a C2 IMO, it may have been in use for 30 years but it may not of carried it's FLC but that's not to say it won't in future.

The circuit isn't classed as a fixed load so therfore needs over current protection. The current protection is over rated so needs coding.
 
708.553.1.12 Each socket-outlet shall be protected by an individual overcurrent protective device, in accordance
with the requirements of Chapter 43
A fixed connection for supply to each leisure accommodation vehicle (including caravans) or tent shall be protected
individually by an overcurrent protective device, in accordance with the requirements of Chapter 43






 
Sorry I should have said that before, each one separately protected by its on Mcb inside the hook up. So the regs mentioned above are satisfied, im just worried about the loops in and out to each point, being on the 63A mcb
 
IMO the 63a requires downrating and code as a code 2.

the 63a doesn't offer protection to the 6mm cable so in the event of high usage the cable could overheat and potentially melt before the 63a breaker trips which could potentially introduce a whole range of other problems.
 

Reply to EICR code in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...
Replies
14
Views
3K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
For emergency use, when there's a power outage, the current situation (no pun intended) is that I'm running a hook up cable from the 16A socket on...
Replies
3
Views
2K
I have had a kitchen extesion built on an old property (c.1810), which has an unusual consumer unit situation. Part of the property has only a...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock