Discuss EICR codes in the UK Electrical Forum area at ElectriciansForums.net

SSE

-
Reaction score
22
Thoughts on the following; no main bond to gas mains (C1), spur spurred of a spur on a ring (C2) & numerous inaccessible sockets for kitchen appliances under worktop with no switched spurs above worktop for isolating sockets (C3). Been a while since I've done an EICR! Thanks in advance.
 
Is this a Report someone else has done or opinions for a Report of your own. I would C2 the first two and probably wouldn't comment on the sockets.
 
Thoughts on the following; no main bond to gas mains (C1), spur spurred of a spur on a ring (C2) & numerous inaccessible sockets for kitchen appliances under worktop with no switched spurs above worktop for isolating sockets (C3). Been a while since I've done an EICR! Thanks in advance.
No gas bond would be a C2, it's not immediately dangerous. I agree with the spur from a spur, but the last one I would probably not code as I can't think of a reg to justify it really.
 
Thoughts on the following; no main bond to gas mains (C1), spur spurred of a spur on a ring (C2) & numerous inaccessible sockets for kitchen appliances under worktop with no switched spurs above worktop for isolating sockets (C3). Been a while since I've done an EICR! Thanks in advance.

Gas bond, C2.
Unfused spur with 2 outlets, maybe a C2 at most, depending on likely loads dependent on their location.
Appliance sockets, no code.
 
The last item is a non compliance with the Scottish Building Stadards. Don't know about your Part P thingy. I'd just mention it in the accompanying correspondence to customer as it's outwith the EICR
 
Thanks very much for your replies chaps. Completely forgot to look back on this thread, the job was put on hold until next week so I forgot to log back on here.
 
Code 1 - according to our niceic area supervisor there are only 3 situations 1 - live exposed conductors 2- incorrect polarity 3 - there was one other cant remember any ideas
Coding is personal opinion, whilst some situations will warrant a specific Coding in most people's eyes it is not for the NICEIC to band about what should be this, that or the other because situations can be variable.
 
i would agree with code 2 and 3 but not with code 1 he is correct in what he is saying i just wish i could remember the third ...
Finding a connection burning would get a code 1 , But then i wou,d make it safe at the time of the inspection as i would with any code 1, so now i have made it safe is it a code 1 any more ???
 
Finding a connection burning would get a code 1 , But then i wou,d make it safe at the time of the inspection as i would with any code 1, so now i have made it safe is it a code 1 any more ???
yes you are obligated to rectify and code 1 on site which then will not stay as code 1 but i would put on report code 1 rectified in order to be able to charge additional .
 

Reply to EICR codes in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Replies
29
Views
4K
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
First : here are 2 x sockets .What code would you give and why ? 3rd pick you can see rear thermal damage on double socket second : Roof...
Replies
32
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
865

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock