The job I mentioned above the bloke is some kind of air-con installer and apparently they always use 2.5mm for 3kw loads!
Pedantic as ever Dave eh? I think you will find 2.5 is extremely common for immersion flexes, FFS how much more does it cost to install a cable that is well over capacity for the load rather than one which is only just over. If I came across a plumber who stuck a bit of 1.5 in I would ask why as well.
 
Pedantic as ever Dave eh? I think you will find 2.5 is extremely common for immersion flexes, FFS how much more does it cost to install a cable that is well over capacity for the load rather than one which is only just over. If I came across a plumber who stuck a bit of 1.5 in I would ask why as well.

Cost is irrelevant. If 2.5mm is squeezed into a terminal designed for a max of 1.5mm then there is a problem.
Do you also install all final circuits in bigger cable for the sake of putting an over capacity cable in?

I installed a ring final in 1.5mm at the weekend as that is what my calculations said would be right, would you have done it in 2.5 and wasted the extra couple of hundred pounds?
 
Cost is irrelevant. If 2.5mm is squeezed into a terminal designed for a max of 1.5mm then there is a problem.
Do you also install all final circuits in bigger cable for the sake of putting an over capacity cable in?

I installed a ring final in 1.5mm at the weekend as that is what my calculations said would be right, would you have done it in 2.5 and wasted the extra couple of hundred pounds?
How many immersion heater heads are designed for 1.5mm? why would you install an RFC in 1.5 was it for a specific application or for general use, RFC's are usually installed in 2.5 as far as I am aware I cant really understand the point you are tying to make??
 
Pedantic as ever Dave eh? I think you will find 2.5 is extremely common for immersion flexes, FFS how much more does it cost to install a cable that is well over capacity for the load rather than one which is only just over. If I came across a plumber who stuck a bit of 1.5 in I would ask why as well.

Why would you ask why to a bit of 1.5 butyal? I never find 2.5 it's always been 1.5 and that's all I've ever done for standard immersion heaters why use anything else
 
Why would you ask why to a bit of 1.5 butyal? I never find 2.5 it's always been 1.5 and that's all I've ever done for standard immersion heaters why use anything else
So that you don't find them suffering from overheating and general degrading over time, given the arduous environments they are often in. If you are running them off an FCU then that's a bad idea anyway as the fuse is at its limit and contributing to the overheating. How much more does a bit of 2.5 cost?
 
2.5 butyal rated at a higher temp then 1.5? Don't think so! As Dave has already said cost is irrelavant
Who said anything about the temperature rating?? 1.5 is rated at 16A, which, given the conditions it is being used in, is running it close. Have you not come across such cables in a bad state after prolonged use? And what's butyal anyway, it is like butyl?
 
Last edited:
How many immersion heater heads are designed for 1.5mm? why would you install an RFC in 1.5 was it for a specific application or for general use, RFC's are usually installed in 2.5 as far as I am aware I cant really understand the point you are tying to make??

As far as I know the standard single phase 3kW immersion is designed for 1.5mm fix, and the cable grip certainly ain't big enough for any bigger flex.
I installed in 1.5mm because it was the right size for the job and I don't suffer from the urge to oversize the cables unnecessarily.
RFCs are subject to a minimum cable size of 2.5 for plastic insulated cables and 1.5 for mineral insulated cables though it is usual to install in 4mm single commercially to meet grouping requirements.
 
Who said anything about the temperature rating?? 1.5 is rated at 16A, which, given the conditions it is being used in, is running it close. Have you not come across such cables in a bad state after prolonged use? And what's butyal anyway, it is like butyl?

You mentioned general overheating and degradation which in my experience is almost always down to the temperature affecting the insulation inside the terminal chamber of the immersion heater. I have never seen a 1.5mm butyl feeding an immersion heater suffer from overheating through overload.
localised heating at the terminations does not necessarily indicate overload or 'running it close', heating through overload is normally visible as a deformation of the insulation and sheath along the length of the cable or localised at bends or other stress points along the run of the cable.

A 3kW 240V immersion heater (2.7kW at 230V) which is the standard these days will draw 12.5A. this is just under 80% of the rated operating current of the cable (16A) I don't see how you can consider that to be running it close? It is only 4/5 of the rated current of the cable!
 
I simply tell the customer they are paying for a report, as I find it. I leave it fully confident that they can get another sparky in if they wish to verify any faults I have highlighted.
 
I fitted 3 lengths of 2.5mm butyl flex to immersion heaters yesterday. I'll let myself off over sizing the cable though as they were 4kW elements. Now that would have been pushing 1.5mm flex to its limit, but a 3kW element certainly wouldn't.
 
I don't see how you can consider that to be running it close? It is only 4/5 of the rated current of the cable

Indeed. For anyone worried about using a cable near rating, remember that the heat dissipated is proportional to the square of the current, in this case 16/25 or about 64% of the permitted temperature rise.

I can see the point in standardising on 2.5 for 3kW aircon loads though as the voltage drop during compressor starting is critical and might often be a more onerous requirement than CCC.
 
Indeed. For anyone worried about using a cable near rating, remember that the heat dissipated is proportional to the square of the current, in this case 16/25 or about 64% of the permitted temperature rise.

Please can you explain this one to me as I've not heard / been taught this calculation / consideration .... sorry if I'm being dumb!

p.s.Can we not just say heat resistant flex rather than butyl ... its so much easier to spell!!:tounge_smile:
 
Please can you explain this one to me as I've not heard / been taught this calculation / consideration .... sorry if I'm being dumb!

p.s.Can we not just say heat resistant flex rather than butyl ... its so much easier to spell!!:tounge_smile:

Butyl has enhanced heat resistance over standard duty flex, but not all heat resistant flex is butyl. Butyl is rubber HR flex but you can get PVC HR flex too.
 
Please can you explain this one to me

P=I²R

This P being the one dissipated in the cable, not the load.
 
Cheers.

I now need to learn to spell butyl correctly then! Lol! Only every used "heat resistant flex" from wholesalers. I'll have a look into when butyl would be prudent in comparison to heat res. flex.

I didn't notice the link between P = I2 x R, so thanks for clarifying for me
 

Reply to EICR on a Sunday in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just your thinking on this… Doing Remedials on a EICR … the DB is a old Wylex with MCB”S/RCD Its a 10 way… rammed packed with cabling,,,the...
Replies
3
Views
1K
I went out today to carry out an EICR on a domestic property. The lead up to the job had been confusing. The elderly (roughly @telectrix 's age)...
Replies
10
Views
2K
So time and again I will get the odd private job to do, and in the future I will want to start my own company. I always find myself getting stuck...
Replies
18
Views
5K
I've done a few EICRs for a landlord and the latest one of his I've given an unsatisfactory, I've advised changing the CU - existing one is old...
Replies
18
Views
2K
I wonder if anyone has some good stories of really easy call-outs made a lot more difficult by the customer's rather fixed views. Here is my...
Replies
39
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock