Discuss EICR question - gas bond off main TNS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

I think I'd be getting the DNO in to sort that 951 clamp on the incomer and possibly the service head as it looks like it may be fused on the neutral as well as the live
 
I think I'd be getting the DNO in to sort that 951 clamp on the incomer and possibly the service head as it looks like it may be fused on the neutral as well as the live on
I think I'd be getting the DNO in to sort that 951 clamp on the incomer and possibly the service head as it looks like it may be fused on the neutral as well as the live
ok thank you.. is this the way they used to do it? It’s seems to be a cut out I’ve never seen before? Would you Earth it from gas clamp straight to CCU instead?
 
ok thank you.. is this the way they used to do it? It’s seems to be a cut out I’ve never seen before? Would you Earth it from gas clamp straight to CCU instead?
At some point it is possible the main earth terminal has been removed for whatever reason, hard to know who fitted the 951 clamp on the incomer but that may be when the MET was removed

It would probably be better to take the bonding to the CU although I would be careful messing around with the 951 clamp on the incomer in case you damage the cable and it may be better to speak to the DNO before doing anything
 

Reply to EICR question - gas bond off main TNS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, it's been a while since I've been on, apologies. I am debating whether I need to replace the bonding to the gas meter. The meter is...
Replies
1
Views
308
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
833

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock