Discuss EICR question, OLD AC RCD- code 3 or no code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Another grey area to the already 50 shades of grey coding

Retrospective / not retrospective / was fine at the time of install / is now out dated and needs changing / tests up fine / tests up fine but doesn't meet the latest version of 7671

My opinion when it comes to A/C RCDs on an existing Install , for the purposes of an EICR i would not Code it so long as it tests up fine , functions with the test buttonetc. It was installed, it met the regs at that time and is fine until further notice
But did you test the RCD while the washing machine was running and leaking DC into the system? Or the EV charge point? Or some other gizmo?
If we are no longer allowed to install an AC RCD, because of the above, surely if we come across one on an EICR, we should be alerting the client to the potential danger by coding it C3.
 
Another grey area to the already 50 shades of grey coding

Retrospective / not retrospective / was fine at the time of install / is now out dated and needs changing / tests up fine / tests up fine but doesn't meet the latest version of 7671

My opinion when it comes to A/C RCDs on an existing Install , for the purposes of an EICR i would not Code it so long as it tests up fine , functions with the test buttonetc. It was installed, it met the regs at that time and is fine until further notice
At last someone who knows
 
Another grey area to the already 50 shades of grey coding

Retrospective / not retrospective / was fine at the time of install / is now out dated and needs changing / tests up fine / tests up fine but doesn't meet the latest version of 7671

My opinion when it comes to A/C RCDs on an existing Install , for the purposes of an EICR i would not Code it so long as it tests up fine , functions with the test buttonetc. It was installed, it met the regs at that time and is fine until further notice
Me and my son (who is also an electrician) were having this discussion and he said much the same as you

I then said - in that instance how would you code a voltage operated ELCB- it complied with the regs at the time of the install and you can test it with an RCD tester and the test button works so....

In my opinion we test to the current regs and make a decision to code accordingly

I was on 2 minds on RCDs that are AC type-
1. note on cert and code 3, suggest change (this is what I have been doing till now)

2. note on cert and code 2, suggest change / replacement, EICR unsatisfactory.

Will be getting my SELECT asessment on Friday so will bring it up then, in the meantime I will email NICEIC and SELECT (I am in both) and get an opinion.
 
Last edited by a moderator:
Me and my son (who is also an electrician) were having this discussion and he said much the same as you

Me and my son (who is also an electrician) were having this discussion and he said much the same as you

I then said - in that instance how would you code a voltage operated ELCB- it complied with the regs at the time of the install and you can test it with an RCD tester and the test button works so....

In my opinion we test to the current regs and make a decision to code accordingly

I was on 2 minds on RCDs that are AC type-
1. note on cert and code 3, suggest change (this is what I have been doing till now)

2. note on cert and code 2, suggest change / replacement, EICR unsatisfactory.

Will be getting my SELECT asessment on Friday so will bring it up then, in the meantime I will email NICEIC and SELECT (I am in both) and get an opinion.

What would be your reasoning behind option #2 in coding this C2?
 
Me and my son (who is also an electrician) were having this discussion and he said much the same as you

Me and my son (who is also an electrician) were having this discussion and he said much the same as you

I then said - in that instance how would you code a voltage operated ELCB- it complied with the regs at the time of the install and you can test it with an RCD tester and the test button works so....

In my opinion we test to the current regs and make a decision to code accordingly

I was on 2 minds on RCDs that are AC type-
1. note on cert and code 3, suggest change (this is what I have been doing till now)

2. note on cert and code 2, suggest change / replacement, EICR unsatisfactory.

Will be getting my SELECT asessment on Friday so will bring it up then, in the meantime I will email NICEIC and SELECT (I am in both) and get an opinion.
IF we all adopted this approach 99% of installs I come across will fail an EICR

That being said it would generate me a huge amount of business replacing loads of boards
 
Me and my son (who is also an electrician) were having this discussion and he said much the same as you

I then said - in that instance how would you code a voltage operated ELCB- it complied with the regs at the time of the install and you can test it with an RCD tester and the test button works so....

In my opinion we test to the current regs and make a decision to code accordingly

I was on 2 minds on RCDs that are AC type-
1. note on cert and code 3, suggest change (this is what I have been doing till now)

2. note on cert and code 2, suggest change / replacement, EICR unsatisfactory.

Will be getting my SELECT asessment on Friday so will bring it up then, in the meantime I will email NICEIC and SELECT (I am in both) and get an opinion.
Why do you think SELECT or the NICEIC will give a meaningful opinion. You are a competent person use your own judgement.
 
But should not we all at least have a point of reference where most of us agree what this is what a Code should be for an A/C type RCD

I do an EICR for a rental today and I say worse case RCD is code 3 so satisfactory to leave as is
Change or tenant 6 months later so new EICR
A another sparks does the EICR and Codes the same RCD code 2 needs changing forth with

We all look a bit daft
 
The latest BPG#4 already has this given as C3 "A Type AC RCD installed where a Type A RCD is required" on page 19

Now we all know that BPG are guidance, not a replacement for the regs or sensible and professional assessment of the situation and real-world risk, but here it makes perfect sense to me. It could and probably should be improved which C3 implies, but equally it is not likely to present a very high risk in the majority of fault situations that C2 merits.

If it were for an EV or PV system not using SWA cable, etc, and against the MI then you might decide for C2.

Same for TT (so OCPD disconnection not likely) and if evidence of the RCD not working as expected, etc. Here the suggestion by @Pretty Mouth for testing using Type A setting on the MFT sounds reasonable, if it fails to trip in required time then C2 would be hard to argue against.
 
C3 doesn't seem unreasonable and it's a code in which I can see logic. It won't result in an unsatisfactory report and raises a potential issue - what's not to like?
There is nothing to say a C3 shouldn't warrant an unsatisfactory Report.
 
Last edited:

Reply to EICR question, OLD AC RCD- code 3 or no code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all. What are your thoughts on coding type AC RCDs when doing EICR's? I understand the issue on DC currents preventing RCd's from functioning...
Replies
10
Views
9K
My builder has sprung a job on me. New circuit required for a hob. The CU has a single 30mA RCD, type AC. I am still unsure exactly when I should...
Replies
4
Views
1K
Hello sparkly people Im a total beginner around how electricity really works. Ive recently been made redundant from ground works in construction...
Replies
2
Views
791
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
764
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock