But did you test the RCD while the washing machine was running and leaking DC into the system? Or the EV charge point? Or some other gizmo?Another grey area to the already 50 shades of grey coding
Retrospective / not retrospective / was fine at the time of install / is now out dated and needs changing / tests up fine / tests up fine but doesn't meet the latest version of 7671
My opinion when it comes to A/C RCDs on an existing Install , for the purposes of an EICR i would not Code it so long as it tests up fine , functions with the test buttonetc. It was installed, it met the regs at that time and is fine until further notice
If we are no longer allowed to install an AC RCD, because of the above, surely if we come across one on an EICR, we should be alerting the client to the potential danger by coding it C3.