Discuss Electric Hand Dryers in the Electrical Appliances Forum area at ElectriciansForums.net

S

sl1210

Got to connect 4 x electric hand dryers tomorrow in 4 x different toilets. Was going to spur off the nearest socket point for each one, with an rcd spur by each dryer, via trunking/conduit.

Silly question, but do they need to be rcd spurred, if there is no shower???

Believe it or not they come with 3 pin plug tops. lol
 
toilet is not a special location, so the requirement for RCD protection only applies if sockets are fitted, as wiring is surface, so 522.6.101 does not apply.
 
so running a surge protected extension lead over the hand basin is a bad idea??? haha

i just thought because of wet hands, and the hand basin maybe rcd protection would be required, although i guess they are double insulated, although the be honest rcd spur units aren't cheap, and if i don't need to fit them then thats great
 
mount them high up then or they'll forever be getting switched off.
 
i know this and was going to put them originally for peace of mind. just wanted to know peoples thoughts.

i underestimated their cost in my quote, but am sure i've allowed more than enough on the labour to cover them. i hope
 
Couldn't you RCD the entire circuit at the consumer unit with an RCBO or separate RCD, rather than having four individuals? These days I think it is normal to RCD everything, unless there is a very good reason not to.
 
I would have thought the sockets were on RCDs anyhow, personally I would wire the handriers on seperate circuits if it wasn't too much hassle, better Job IMO.
 
its a small building that teaches english to foreigners. no rcd protection. fuseboards are old mcb types so you cant get rcbo's for them.

believe it or not the fuse boards for 2 of the 4 toilets are, yes you guessed it, in a door inside the toilet. lol. so could possibly supply them 2 direct from fuse board, although don't think there are spare ways
 
Fixed equipment, and not a special location, no need for RCBO unless disconnection times cannot be met IMO, however I would fit RCBOs if they were obtainable.
 
Just a thought, do the manf's instructions stipulate RCD protection required? Daz
 
i haven't looked mate. but i'm gonna put them anyway for piece of mind. i've managed to fine some for £16 each at screwfix ;)

Make sure that the circuit that you are joining in to isn't RCD protected before you fit RCD spurs, or you may end up going backwards and forwards to reset one or the other due to discrimination.

Cheers.............Howard
 

Reply to Electric Hand Dryers in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

VELAIR HAND DRYERS NOW STOCKED! Velair hand dryers are a popular choice in the world of hand-drying solutions. These hand dryers are known for...
Replies
0
Views
879
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
567
An odd question granted but bear with me. I've got to extend a radial circuit in a community centre to fit a new hand dryer in the toilets, but I...
Replies
15
Views
3K
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
388
Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Replies
12
Views
543

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock