- Reaction score
- 8,894
To be fair to the inspector, I could have done with re-reading section E (overall summary) at the end. That bit is well written and I think by the time I'd sifted through everything else I'd forgotten about it. It's a bit unusual to get more useful information from that box than the rest of the report but It does demonstrate that the person inspecting it had a clear view of the most pressing issues.
On that basis I trust more of the report now, and retract my comment to start again.
If the £700 quote is to replace a consumer unit, rewire the lighting circuit (two floors?), find and address the break in the ring final circuit, investigate the low IR issues and resolve, and add bonding to services, I actually don't consider it too bad at all. There are a few open-ended tasks in that that might take minutes or hours.
On that basis I trust more of the report now, and retract my comment to start again.
If the £700 quote is to replace a consumer unit, rewire the lighting circuit (two floors?), find and address the break in the ring final circuit, investigate the low IR issues and resolve, and add bonding to services, I actually don't consider it too bad at all. There are a few open-ended tasks in that that might take minutes or hours.