Discuss EMINoise filter amp ratings? in the UK Electrical Forum area at ElectriciansForums.net

damunk

-
Reaction score
2
if a servo driver has a amp rating of 9.5 amp single phase 240V and peak current at 30amp
what amp rating should be chosen for a emi power/line filter? thank you.
 
if a servo driver has a amp rating of 9.5 amp single phase 240V and peak current at 30amp
what amp rating should be chosen for a emi power/line filter? thank you.
also can you use just one line filter for 4 servos or is it okay to use 4 seperate ones , one for each servo
 
If the servos are close together you can use a single EMI filter. If further apart then it is an occasion where the likes of CY cable (copper braid shield) is useful to contain noise before it is filtered, but it has to be properly earthed using the correct glands to be effective.

Generally speaking an EMI filter would be need to be rated at max continuous load, and for something where the load is not fixed the safest option is to be rated at the supply OCPD (so >= 13A if 13A fuse, or >= 16A if 16A MCB, etc)
 
If the servos are close together you can use a single EMI filter. If further apart then it is an occasion where the likes of CY cable (copper braid shield) is useful to contain noise before it is filtered, but it has to be properly earthed using the correct glands to be effective.

Generally speaking an EMI filter would be need to be rated at max continuous load, and for something where the load is not fixed the safest option is to be rated at the supply OCPD (so >= 13A if 13A fuse, or >= 16A if 16A MCB, etc)
cant i just buy 4 of those good quality tdk lambda filters for each servo and bolt themsecurley to panel to get brilliant grounding.?
 
cant i just buy 4 of those good quality tdk lambda filters for each servo and bolt themsecurley to panel to get brilliant grounding.?
Yes, if drives and filters can be grounded to a metal base plate you will get the best results.

Some drives also specify screened cables to the motor though as the output waveform can be very full of HF noise, so check for that.
 
Yes, if drives and filters can be grounded to a metal base plate you will get the best results.

Some drives also specify screened cables to the motor though as the output waveform can be very full of HF noise, so check for that.

Guys RSEN"2030D but they are from US and the postage will be pretty big. I have been told these TDK emi filters are very good.
Anyone can receommend some emi filters than will 100% be good as tdk ones,
 

Reply to EMINoise filter amp ratings? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
743
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
567
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
854
I will describe my problem in as much detail so you guys might be able to answer my question. I am never home, my Electric bill is $ 28 to $30 a...
Replies
23
Views
1K
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
480

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock