    Evening evening!

    Been giving drawings for some flats which also need 3x ev charging points outside
    no spec given atall as yet!

    Just wanting to get clued up before hand

    so for something like this- Rolec EV Charging IEC WallPod 16A HomeCharge EVWP2010 | RS Electrical Supplies - http://www.rselectricalsupplies.co.uk/rolec-ev-charging-iec-wallpod-16a-homecharge-evwp2010_9486

    simply just a 16a SWA radial on a mcb as the unit has the built in rcd (is it A type?)
    if the system is TN- then am i right in thinking I need a rod for each of the chargers

    cheers for any insight
     
  2. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    I would wait before commenting until you get hold of the specification for these units.
     
    • Agree Agree x 1
  3. westward10
    Offline

    westward10 Time is like a hound snapping at my heels. Electrician's Arms

    Location:
    Northamptonshire
    See Section 722 of BS7671, the IET also have the Code of Practice for Electric Vehicle Charging Equipment.
     
    • Like Like x 1
  4. ruston
    Offline

    ruston Trusted Advisor

    Location:
    Northumberland
    I was about to post the same , but I am having trouble scrolling and posting on the site .
    I am using opera , and have just tried IE.
    Ie was ok before ,but is now doing the same .
     
  5. dmxtothemax
    Offline

    dmxtothemax Regular EF Member

    Location:
    Australia
    DITTO !
    I would look into it carefully first
    especially the amount of power used 16 A seems a little light on !



    What is a Tesla Wall Connector?
    The Wall Connector can be installed on a circuit from 6 to 32 amps
     
  6. ruston
    Offline

    ruston Trusted Advisor

    Location:
    Northumberland
  7. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Believe its with PME supply, where TT is suggested, albeit there's a get out of jail card in reg 722.411.4.1!

    If I was doing some, I would purchase and read the COP, as westward suggested.
     
  8. J.C.E
    Offline

    J.C.E Electrician's Arms

    Location:
    Earth
    are you referring to 722.411.4.1iii ?
    is this a 'a type rcd'?
     
  9. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Nope not exactly;

    722.411.4.1, 'The requirements of this regulation need not be applied for charging point at a dwelling, if none of (i), (ii) or (iii) is reasonably practicable'.

    Seem to remember there was another thread on this subject, not so long ago, where that sentenced was debated back and forth. I still don't understand it.

    As said, never done one before, but if I did, think I would obtain that COP and have a good read.
     
    • Like Like x 1
  10. J.C.E
    Offline

    J.C.E Electrician's Arms

    Location:
    Earth
    also goes on to say what their def of dwellings is......would 9 flats over 3 stories be classed as dwelling?
     
  11. westward10
    Offline

    westward10 Time is like a hound snapping at my heels. Electrician's Arms

    Location:
    Northamptonshire
    That would be nine dwellings.
     