Evening evening!

Been giving drawings for some flats which also need 3x ev charging points outside
no spec given atall as yet!

Just wanting to get clued up before hand

so for something like this- Rolec EV Charging IEC WallPod 16A HomeCharge EVWP2010 | RS Electrical Supplies - http://www.rselectricalsupplies.co.uk/rolec-ev-charging-iec-wallpod-16a-homecharge-evwp2010_9486

simply just a 16a SWA radial on a mcb as the unit has the built in rcd (is it A type?)
if the system is TN- then am i right in thinking I need a rod for each of the chargers

cheers for any insight
 
Evening evening!

Been giving drawings for some flats which also need 3x ev charging points outside
no spec given atall as yet!

Just wanting to get clued up before hand

so for something like this- Rolec EV Charging IEC WallPod 16A HomeCharge EVWP2010 | RS Electrical Supplies - http://www.rselectricalsupplies.co.uk/rolec-ev-charging-iec-wallpod-16a-homecharge-evwp2010_9486

simply just a 16a SWA radial on a mcb as the unit has the built in rcd (is it A type?)
if the system is TN- then am i right in thinking I need a rod for each of the chargers

cheers for any insight
I would wait before commenting until you get hold of the specification for these units.
 
See Section 722 of BS7671, the IET also have the Code of Practice for Electric Vehicle Charging Equipment.
 
I was about to post the same , but I am having trouble scrolling and posting on the site .
I am using opera , and have just tried IE.
Ie was ok before ,but is now doing the same .
 
DITTO !
I would look into it carefully first
especially the amount of power used 16 A seems a little light on !



What is a Tesla Wall Connector?
The Wall Connector can be installed on a circuit from 6 to 32 amps
 
Evening evening!

Been giving drawings for some flats which also need 3x ev charging points outside
no spec given atall as yet!

Just wanting to get clued up before hand

so for something like this- Rolec EV Charging IEC WallPod 16A HomeCharge EVWP2010 | RS Electrical Supplies - http://www.rselectricalsupplies.co.uk/rolec-ev-charging-iec-wallpod-16a-homecharge-evwp2010_9486

simply just a 16a SWA radial on a mcb as the unit has the built in rcd (is it A type?)
if the system is TN- then am i right in thinking I need a rod for each of the chargers

cheers for any insight

Believe its with PME supply, where TT is suggested, albeit there's a get out of jail card in reg 722.411.4.1!

If I was doing some, I would purchase and read the COP, as westward suggested.
 
are you referring to 722.411.4.1iii ?
is this a 'a type rcd'?

Nope not exactly;

722.411.4.1, 'The requirements of this regulation need not be applied for charging point at a dwelling, if none of (i), (ii) or (iii) is reasonably practicable'.

Seem to remember there was another thread on this subject, not so long ago, where that sentenced was debated back and forth. I still don't understand it.

As said, never done one before, but if I did, think I would obtain that COP and have a good read.
 
Nope not exactly;

722.411.4.1, 'The requirements of this regulation need not be applied for charging point at a dwelling, if none of (i), (ii) or (iii) is reasonably practicable'.

Seem to remember there was another thread on this subject, not so long ago, where that sentenced was debated back and forth. I still don't understand it.

As said, never done one before, but if I did, think I would obtain that COP and have a good read.
also goes on to say what their def of dwellings is......would 9 flats over 3 stories be classed as dwelling?
 

Reply to EV charging points advise needed in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Afternoon all, and apologies if this has been covered elsewhere, but a search didn't bring anything up. Just a quick heads up to anyone...
Replies
3
Views
2K
So I am a fully qualified spark with my own company, however I also have a few properties I rent out. One of my tenants asked if they can have an...
Replies
84
Views
10K
As the title says, does a three-pin socket (external) used as charging point need an earth electrode or open PEN fault? Are mode 1 and mode 2...
Replies
17
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock