You brainy guys may be able to help with this thought I was having.
There has been a thread recently about 4mm radial from ring main.

This got me thinking..... (No funny comments)
So my question is: If you had a building/garage/shed, say about 5 meters away from a house, is it acceptable to extend one of the RFC's to this building?

I know its best to have it's own circuit, but just for this conundrum lets say there are no spare ways in the CU.
Yes you could use a 13A fused spur, but what if you wanted to have a few appliances in there that would draw more than 13A.

You would also be within the 100m area as well.
 
Nothing to stop you from doing it, not ideal though.

Totally agree mate, its not ideal.
I was just thinking of different ways of doing things. Never thought of extending a RFC to something what was not part of the house.
It's something that I have not read about on here... That's why I asked.
 
Agreed. So long as the cables are suitably protected, the only real down-side is the lack of fault separation, or having an independent means of isolation.
 
You brainy guys may be able to help with this thought I was having.
There has been a thread recently about 4mm radial from ring main.

This got me thinking..... (No funny comments)
So my question is: If you had a building/garage/shed, say about 5 meters away from a house, is it acceptable to extend one of the RFC's to this building?

I know its best to have it's own circuit, but just for this conundrum lets say there are no spare ways in the CU.
Yes you could use a 13A fused spur, but what if you wanted to have a few appliances in there that would draw more than 13A.

You would also be within the 100m area as well.
Extend the RFC in 2.5MM2 no point in changing cable size half way through a circuit, no point whatsoever
 
the problem with doing that, if unfused, is that although the 4mm cable may be OK for 32A, you're running the risk of taking 32A from 1 point on the RFC. this is the whole capacity of the RFC without other outlets being considered, and, if the point where it's tapped off is close to 1 end of the RFC, then almost all of the 32A would be carried by the short leg. best to fit FCU and use 2.5mm cable for the spur, or redesign to provide a separate circuit.
 
I was just thinking of, is it acceptable to extend the RFC using 2.5mm to another building close to the house, like a garage/shed. Then the RFC is also in there for the appliances.
So basically use 5 core SWA cable from socket in house to outbuilding. It's still a ring... but extended.
 
I was just thinking of, is it acceptable to extend the RFC using 2.5mm to another building close to the house, like a garage/shed. Then the RFC is also in there for the appliances.
So basically use 5 core SWA cable from socket in house to outbuilding. It's still a ring... but extended.
The cpc wont be a ring though will it? 6 core maybe.
 
I was just thinking of, is it acceptable to extend the RFC using 2.5mm to another building close to the house, like a garage/shed. Then the RFC is also in there for the appliances.
So basically use 5 core SWA cable from socket in house to outbuilding. It's still a ring... but extended.
Must admit that I have done this. Run a short section of 5C SWA from a metal clad garage socket a couple of metres out under a path and into a shed to another metal clad socket then continue the ring round the shed. CPC and armour all connected at each end of the SWA so end to CPC readings would be inaccurate and lower. If honest, not totally happy as ideally would be nice to be able to isolate shed. RFC in garage was small and not one of the main house circuits. Does anyone make a four pole isolate switch?
 
The cpc wont be a ring though will it? 6 core maybe.

Glad you mentioned that mate. I was wondering if the earth had to be a ring as well.
All theoretical this anyhow, but I'm learning stuff, so all is good.

Regarding the isolation of the supply to the garage/shed, you could use a 4 pole changeover isolator. So in the 'off' position the garage/shed supply is isolated..
 
Would that matter? Assuming cpc meets adiabatic requirements throughout the circuit, and is taken to every point in the circuit?

This is where I wasn't sure so suggested a 5 core, hoping someone would correct me if I was wrong.
 
Regarding the isolation of the supply to the garage/shed, you could use a 4 pole changeover isolator. So in the 'off' position the garage/shed supply is isolated..
That is a good point as you don't want the ring opened to isolate! Problem is many are centre-off which is not what you really want.

This might be usable (4P with NO/NC contacts), but you would need a separate box and knob to complete it. at 25A it ought to match the 2.5mm cable's rating:
 
This is where I wasn't sure so suggested a 5 core, hoping someone would correct me if I was wrong.
I'm not sure myself tbh, which is why i worded it as a question. Have to check the regs. I was led to believe that a ring could be run in conduit or trunking, using containment as CPC, where there's no need for it to make a ring. Would the same not apply in this case?
 
That is a good point as you don't want the ring opened to isolate! Problem is many are centre-off which is not what you really want.

This might be usable (4P with NO/NC contacts), but you would need a separate box and knob to complete it. at 25A it ought to match the 2.5mm cable's rating:

This says its a 4 pole changeover isolator but the data sheet doesn't???? Or I'm tired and missing something.
 
This is where I wasn't sure so suggested a 5 core, hoping someone would correct me if I was wrong.
The problem with not having the CPC in a ring as well is for testing: you won't easily detect an open on the CPC and so a reduction in its fault capacity & reliability.

But you could run an external CPC with 4-core SWA and have the CPC loop through the armour and back via the separate CPC (or 5th core).
[automerge]1590442220[/automerge]
This says its a 4 pole changeover isolator but the data sheet doesn't???? Or I'm tired and missing something.
Centre-off! You don't want the ring left open.
 
Aha. Here's the relevant reg:

543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the conductors of the ring, the circuit protective conductor of every ring final circuit shall also be run in the form of a ring having both ends connected to the earthing terminal at the origin of the circuit.
 
Aha. Here's the relevant reg:

543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the conductors of the ring, the circuit protective conductor of every ring final circuit shall also be run in the form of a ring having both ends connected to the earthing terminal at the origin of the circuit.
so the armour of SWA is "a metal covering containing all of the conductors of a ring"?????
 
so the armour of SWA is "a metal covering containing all of the conductors of a ring"?????
I would say so. And as I guess you need accessible junction box then you would have a means of checking the 2nd ring's CPC continuity.

But more importantly, what do we call this arrangement?

An hourglass circuit? It is a curious way of passing the time discussing it...
 
so the armour of SWA is "a metal covering containing all of the conductors of a ring"?????
I'm not sure it would be. The reg does seem to back up Pete's post.

Would it be a reasonable departure from the regs to extend the ring to the outbuilding using 4C SWA, using armour as CPC? Again, assuming adiabatic, max zs, etc met. It would add an extra layer or 2 to the testing, but I don't think it would be less safe.
 
That is a good point as you don't want the ring opened to isolate! Problem is many are centre-off which is not what you really want.

This might be usable (4P with NO/NC contacts), but you would need a separate box and knob to complete it. at 25A it ought to match the 2.5mm cable's rating:
Very good point. You don’t want an isolator that in effect breaks the first part of the ring into two legs and cuts off the latter part.
 
It would add an extra layer or 2 to the testing, but I don't think it would be less safe.

I think those aspects are connected. Once you have installed a non-standard configuration, other people might have to test, modify and repair it. If they don't understand it or make incorrect assumptions about it, they might not test it correctly (or at all, if they keep getting nonsense readings) hence it might become less safe.

Personally I would be disappointed to find a ring extended to an outbuilding simply for economy, however if the lengths and loading are sensible, I would accept it. There is a risk that if the garage run adds much length at one end of the ring, and is perhaps only occasionally used, most of the house loading would end up on one leg. But I also accept that it is very rare for a correctly-installed ring cable to be overloaded under normal operating conditions.

The 5-core idea is a bodge. There's no reason to do anything that weird with the CPCs when you could just use 7-core SWA and give both legs three cores. I would be tempted to connect the armour to the spare core at both ends but both to one CPC at one end only, so that the readings come out correct for equal-size conductors.
 
To be able to isolate the shed, instead of spurring from a 13A fuse, could you spur from a garage board or enclosure, in the house, with maybe a 32A breaker? And going out in 4mm? The supply side coming from the rfc

Wouldnt look terribly great in the house though.
 
I think those aspects are connected. Once you have installed a non-standard configuration, other people might have to test, modify and repair it. If they don't understand it or make incorrect assumptions about it, they might not test it correctly (or at all, if they keep getting nonsense readings) hence it might become less safe.
I hear what you're saying Lucien, though I believe the skills needed to recognise a circuit installed in this manner are quite basic. They would be the same skills needed to recognise and locate parallel paths across the cpc of a ring final. With it being documented as a departure, I would question the competence of anyone unable to understand it.
 

Reply to Extend RFC to a detached building/garage/shed? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've had a search, and found an old thread from 2016... but was wondering about modern views on this situation. I've come into possession of...
Replies
5
Views
398
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
809
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
776
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
374

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock