Thread reopened early because I'm off to bed.

By the way, did anyone notice the Pink Floyd song they sneakily slipped into that Muzak track?
 
By saying no continuity do you mean low ohms measurement between MET and riser is off the scale (Im guessing greater than 200 ohms)

But insulation resistance between MET and riser is 0.00 Mohms.

Is that right? otherwise the information contradicts itself because no continuity wouldnt give a reading of 0.00 Mohms and maybe where the confusions is.
 
The key point of the original question I think is is there an exposed conductive part, a live part (even if covered), or another bonded extraneous conductive part within 2.5 m of the hatch giving access to the riser.
The majority of the riser is inaccessible and therefore cannot introduce a potential; if the access hatch is not near any conductive part that may become live and can be simultaneously touched by a person or livestock, then the part at the hatch will also not be able to introduce its potential into the installation and bonding would not be necessary.

I think what Ian1981 is saying about measurements is as described in the below diagram. The riser is connected to true earth, but not connected to the installation protective conductors.
Extraneous not connected to installation.jpg
 
no i'm confused ( doesn't take much). in OP's post #4, he says:
Testing from the MET or rather the source of earthing to said pipe.
Main earthing conductor disconnected from source earth
IR set to 500v reading of 0.00 Mohms
Also no continuity between said pipework and a known earth source

so... riser is 0.00 M to MET and no connection to earth. that says it's not extraneous.?????
 
no i'm confused ( doesn't take much). in OP's post #4, he says:
Testing from the MET or rather the source of earthing to said pipe.
Main earthing conductor disconnected from source earth
IR set to 500v reading of 0.00 Mohms
Also no continuity between said pipework and a known earth source

so... riser is 0.00 M to MET and no connection to earth. that says it's not extraneous.?????
The OP has apparently changed his mind.
 
no i'm confused ( doesn't take much). in OP's post #4, he says:
Testing from the MET or rather the source of earthing to said pipe.
Main earthing conductor disconnected from source earth
IR set to 500v reading of 0.00 Mohms
Also no continuity between said pipework and a known earth source

so... riser is 0.00 M to MET and no connection to earth. that says it's not extraneous.?????
I think perhaps the post might be worded better as

Testing not from the MET but from the source of earthing, whilst it is disconnected from the MET, to said pipe.
IR set to 500V reading 0.00MΩ.

When testing from a known earth internal to the installation to the said pipework there was no continuity.


This is what has been said in post 19.

The pipe is (presumably) buried in the ground and so has very good contact with the ground and therefore shows up as an effective earth rod. However the pipe according to the continuity readings is not connected to the installations earth wiring i.e. it has not been bonded nor has it got a connection with any cpc.
Therefore the pipe is at earth potential but the issue is does it introduce that potential into the installation.
 
Therefore the pipe is at earth potential but the issue is does it introduce that potential into the installation.

or does it introduce an earth potential into the building? and if so, can it be touched? that seems to be the £64,000 question.
 
A "dry riser" is a vertical pipe that usually starts at ground floor level and has an outlet on each floor. Its purposes is to allow firefighters to connect at ground level and the fire level without having to run hose in stairwells.

At no point would it enter the "ground". Effectively, its just a bit of metal within the building. Unless someone has made some sort of connection, then I would be surprised if it tests as extraneous.
 
The key point of the original question I think is is there an exposed conductive part, a live part (even if covered), or another bonded extraneous conductive part within 2.5 m of the hatch giving access to the riser.
The majority of the riser is inaccessible and therefore cannot introduce a potential; if the access hatch is not near any conductive part that may become live and can be simultaneously touched by a person or livestock, then the part at the hatch will also not be able to introduce its potential into the installation and bonding would not be necessary.

I think what Ian1981 is saying about measurements is as described in the below diagram. The riser is connected to true earth, but not connected to the installation protective conductors.
View attachment 43000
Didn’t realise it’s thread is still running but yes Richard you are correct
 
I think perhaps the post might be worded better as

Testing not from the MET but from the source of earthing, whilst it is disconnected from the MET, to said pipe.
IR set to 500V reading 0.00MΩ.

When testing from a known earth internal to the installation to the said pipework there was no continuity.


This is what has been said in post 19.

The pipe is (presumably) buried in the ground and so has very good contact with the ground and therefore shows up as an effective earth rod. However the pipe according to the continuity readings is not connected to the installations earth wiring i.e. it has not been bonded nor has it got a connection with any cpc.
Therefore the pipe is at earth potential but the issue is does it introduce that potential into the installation.
Correct again
 
A "dry riser" is a vertical pipe that usually starts at ground floor level and has an outlet on each floor. Its purposes is to allow firefighters to connect at ground level and the fire level without having to run hose in stairwells.

At no point would it enter the "ground". Effectively, its just a bit of metal within the building. Unless someone has made some sort of connection, then I would be surprised if it tests as extraneous.
The dry riser comes out of the ground all metallic in construction and does introduce an earth potential.
It is a separate service entering the building and not in anyway connected to the main buildings water supply.
 

Reply to Extraneous conductive parts in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

During an EICR I have come across a metal tap and copper pipes supplied by a blue plastic pipe. This measures 0.022 MegOhms, this is directly...
Replies
24
Views
3K
I'm probably displaying my ignorance here, but fortunately I'm not one of those people who can't stand to be laughed at! I've been thinking a bit...
Replies
27
Views
1K
During an EICR I have found an isolator with no cpc present bolted to a large metal post and all the motorized metal car park gate, the fact that...
Replies
22
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
467
Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock