Discuss Fault finding on ring final circuit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
51
Fault finding on ring final, is this the readings you would expect to achieve and are these the correct way to find them thanks

1568C8E7-FCD1-4450-AE68-637CDA06B574.jpeg


10A5C758-49EA-4891-9684-94ED5F9EDC04.jpeg
 
3rd year apprentice don’t do much fault finding
Then to aid us in helping perhaps you could update your profile and avoid unnecessarily obtuse answers.
If you are in training then I suggest you apply for access to the trainee area, lots of help on there from Mentors me included.
 
I don’t fault find at work so pointless asking my boss and it’s for AM2 in few weeks and college have too many people to bother about showing me
Have you looked at the video yet? that should help know end, not much of a Boss if you feel you can't ask him a question, decent people won't mind answering a legitimate question. Where are you based? Sorry missed that London too far for me to come and help you out.
 
Have you looked at the video yet? that should help know end, not much of a Boss if you feel you can't ask him a question, decent people won't mind answering a legitimate question. Where are you based?
Yes I’ve watched it, just wanted to know as in AM2 your only allowed continuity tester so all faults are wiring it’s just the same as dead testing just wanted to know if my drawings was correct
 
Seems odd to me that they only allow a continuity tester, the correct way would be to get resistance readings r1 r2 and rn and then do a figure of 8 R1+R2 reading that would prove your RFC is complete and OK.
 
Pete's approach above is the best one, it will catch most faults, but as you only have a continuity tester:
Reverse polarity:
Normally easiest to find by inspection.
Assuming you have correct end to end resistance results, Joining two poles at the board one of which is not the expected reversed polarity and testing at the socket fronts should give one socket with OL result all others should be very low resistance.
Your diagram and method will work.

Open circuit:
discovered by end to end testing, join one non continuous core to a continuous core and test between the cores at each socket, when you get OL result this is where the fault exists (or the socket beforehand on the outgoing core).
Your diagram and method will work so long as only one leg is joined.

High resistance:
Similar method to open circuit but where the resistance rises is where the fault is (or the socket before hand).
Your diagram and method will work.

Short circuit:
testing between disconnected cores at board the low resistance reading indicates the faulty cores, break the ring down half and half again testing each time between the faulty cores until the fault is narrowed down.
Your diagram and method will not work. only the bit about breaking the ring applies, adding another short circuit to the circuit will not help.
 
Pete's approach above is the best one, it will catch most faults, but as you only have a continuity tester:
Reverse polarity:
Normally easiest to find by inspection.
Assuming you have correct end to end resistance results, Joining two poles at the board one of which is not the expected reversed polarity and testing at the socket fronts should give one socket with OL result all others should be very low resistance.
Your diagram and method will work.

Open circuit:
discovered by end to end testing, join one non continuous core to a continuous core and test between the cores at each socket, when you get OL result this is where the fault exists (or the socket beforehand on the outgoing core).
Your diagram and method will work so long as only one leg is joined.

High resistance:
Similar method to open circuit but where the resistance rises is where the fault is (or the socket before hand).
Your diagram and method will work.

Short circuit:
testing between disconnected cores at board the low resistance reading indicates the faulty cores, break the ring down half and half again testing each time between the faulty cores until the fault is narrowed down.
Your diagram and method will not work. only the bit about breaking the ring applies, adding another short circuit to the circuit will not help.
Thanks so open circuit connect at board end eg. L+N then test at socket between L+N if I get reading OL then open circuit or can do end to end on each socket eg test L to L from socket 1 to 2,
Short circuit, so break ring in half then test end to end at each socket no r1+r2 as this is just adding another short circuit
 
don't over think. thast's a major problem.

a ring is just that. . 3 pieces of wire. you have 3 bits of wire with both ends at the CU. end 1 should connect to end 2, and not connect to the others. sssssimplesss.
 
I had a NICEIC book once upon a time all about fault finding and solutions to identify and solve the faults etc... not sure what happened to it???? but it was very useful when i started out. i bought it at a carboot for hardly anything and paid for itself many times over... Anybody know if the NICEIC are still making upto date versions of the little help books?
 
Thanks so open circuit connect at board end eg. L+N then test at socket between L+N if I get reading OL then open circuit or can do end to end on each socket eg test L to L from socket 1 to 2,
Short circuit, so break ring in half then test end to end at each socket no r1+r2 as this is just adding another short circuit
No such animal as r1+r2 It's R1+R2 which is the figure of 8 reading after you have done end to end r1,r2 and rn and inter connected the conductors as per the video instructions
 
Bradley if your doing your AM2 my only advice is if you locate a fault but don’t think it could be that simple don’t panic or over think things. One of the faults we had thrown at us was a blown lamp on a lighting circuit. And yes you couldn’t remove said lamp to test it properly. I will have a look through some of my books to see if they have pics and easy explanations for you.
 
Bradley if your doing your AM2 my only advice is if you locate a fault but don’t think it could be that simple don’t panic or over think things. One of the faults we had thrown at us was a blown lamp on a lighting circuit. And yes you couldn’t remove said lamp to test it properly. I will have a look through some of my books to see if they have pics and easy explanations for you.
Thanks I’ve done build today have 1 circuit left and then testing and then fault finding either tomorrow or wednesday
 
.. Fault finding is a key skill, learnt on the job, from others .....
Welcome to the 21st century, where real-world simulation software can train and test you on electrical troubleshooting (Fault finding) by creating so many simulated faults for you to troubleshoot, it would take you literally years to gain that experience OJT. (Our mother company sells the electrical troubleshooting training and testing software series.)
 
I find it is easiest to break the ring in the middle and also at the board. You are then left with two radial circuits, easier to work with.
Yeah that’s what I did I passed everything else but failed fault finding when I was doing ring I was looking for either cross polarity or open or short circuit and believe it or not the fault was a high resistance took me ages to find it
 
Bradley if your doing your AM2 my only advice is if you locate a fault but don’t think it could be that simple don’t panic or over think things. One of the faults we had thrown at us was a blown lamp on a lighting circuit. And yes you couldn’t remove said lamp to test it properly. I will have a look through some of my books to see if they have pics and easy explanations for you.
Why not?.....that's the fault.
 
If a lamp has blown you'll get no difference to any readings, L and N are clear anyway. Are you testing each switch circuit to see if lamps are OK?.....so basic it's weird!
 
If a lamp has blown you'll get no difference to any readings, L and N are clear anyway. Are you testing each switch circuit to see if lamps are OK?.....so basic it's weird!
No idea my fault was on intermediate lights was the lights wasn’t working as a intermediate should and the fault was no continuity between of the strappers on the last switch
 
No idea my fault was on intermediate lights was the lights wasn’t working as a intermediate should and the fault was no continuity between of the strappers on the last switch
So, was it incorrectly connected, a faulty switch connection or a damaged/broken conductor?
 
Welcome to the 21st century, where real-world simulation software can train and test you on electrical troubleshooting (Fault finding) by creating so many simulated faults for you to troubleshoot, it would take you literally years to gain that experience OJT. (Our mother company sells the electrical troubleshooting training and testing software series.)

Bold statements in here, not that it would really help ....

Are you here advertising?
 
Bold statements in here, not that it would really help ....

Are you here advertising?
It'd be useful for a house basher, that....millions of fault possibilities, some, I'm sure, completely unheard of, even by the boffins.
 

Reply to Fault finding on ring final circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
513
What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 . The lights are.67 and the is...
Replies
7
Views
703
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
516

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock