Discuss Fault finding single phase motors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

D

daiplayer

Ok got called in regards to somebody's electrica gate not working.

Power supply all seems good.

After removing the motor i attempted to test the windings. ( i really havent done much with motors)

the motor is single phase. Has a N , 2 feeds/supplys/windings. ? is this one :- Electric Gates Accessories, Replacement Liftmaster Sub300 Motor - Gateauto

Ok firstly i tested the other working motor. :

- one winding to N - 34 ohm
- other winding ( reverse winding ?) -N 34 ohms.

On faulty motor :-

- One winding -N 145 ohm
- other winding - N - infinite/open circuit

Am i correct in saying the this motors windings are F****** ?
 
I worked with a company that got such a good discount it was only big motors that got rewound as it was more cost effective to buy a new motor as the down time was minimal
 
Anything below 20HP just went in the skip. As you say, time is a big factor.

Agreed I had a motor with noisy bearings but it was the main kitchen extract so we bought a new motor and the down time was 1 hour if we had taken it out for repair it would have been most of the day but as a wee project we refurbished the old motor
 
Thanks all. :)
Out of interest and a need to learn:) ....
Anybody know what sort of motor this is ?
It has a 10uf capacitor connected at its power supply . Is this just for power factor correction?
How deos this motor reverse? Is it a complete separate winding then?
 
reversing is usually achieved by reversing the start winding wrt the run winding.
 
Permanent capacitor?
Capacitor start?

Can't tell with out more info.

BTW had you said this at the start my answer would have been different
 
yes permanent capacitor , have been trying to find wiring instructions as i cant remember where the capacitor was connected . was def at the power source though.
 
Motorised automatic gates are notorious for breakdowns, and even when repaired, and left working perfectly will have a tendency to fail again quickly, making you look as if you don't know what your doing to the client!!.... In future avoid them like the plague!! lol!!
 
They may also be bad news to work on regards their design
There was a toddler killed here in Maesteg,it was caused by bad design and there are quite a lot about of a similar standard apparently

When working on these contraptions I suppose that the function of the gatestops and their support structures should be confirmed as safe before doing repairs,just in case of potential problems iwith their design and your own responsibilities
 
funny enough i had a look at how the other gate was operating , although they had safety photocells , the closing force on each gate was set way up !! only for small iron gates too. so turned it down by more than half.
 

Reply to Fault finding single phase motors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Replies
2
Views
562
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
684
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
688
I have a single phase stainless steel pasteuriser that has two control boxes attached to it. One box houses the control for the electronics and...
Replies
2
Views
696
I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock