- Reaction score
- 17,080
With regards the 'damaged' cable, I cant remember the IR results precisely however they were a little below 1MΩ to earth. I am unsure of what I could do regards this cable as the 19 core is laid under a shed and concrete, it is about 15m's in length and all other cores are in use. What would you do Richard? This cable is required and the client is not going to agree to the cattery being dug up, there is also no viable option to lay a new cable. Thinking about it further, it will not be touching the armour as the IR results were only just below 1MΩ, still a fail though!
I have not tried Pen 4 in another RCBO by itself, I will do. I did ramp the RCBO and it was fine. Also I will try your suggestion regards seeing if there is voltage on pen1 with pen 4 connected.
I had been at the cattery for 10 hours and I had got to the point where my brain was not working properly so I left. This is one of the few times when a fault is getting the better of me and I'm finding it quite frustrating. I shall go back with a clear head and slowly and methodically test.
Edit... Sorry, quoted too many people!
Spin.. All circuits utilise existing 19 core.
Dave.. my reply to Richard half answers your question. I realise you are a stickler for doing things correctly, but would you really insist to the owner that he dismantle his shed, rip up the concrete etc for an IR result of a little below 1MΩ?
15mtrs of PVC or XLPE insulated cable must be pretty badly damaged to get such an IR reading. Don't just blindly follow a number in a book, think about what it actually indicates in real terms.
No I wouldn't insist on dismantling a shed or ripping up concrete. I would find an alternative route for replacement cables