I have an electrical socket that hasn't worked since we moved into our unit (4 years ago). I finally decided to take a look and see what was going on.

The outlet has a very low voltage coming into it... about 4V according to my multi-meter. I tested the wires coming into the outlet box and I get the same readings - so it's not the outlet itself. There are two sets of neutral/hot wires connected to the outlet. They all give the same reading. I don't know where they go next - everything else in the room works as expected and there are no other improperly functioning outlets in the house. I've tried all the switches in the room and they don't have any effect on the outlet.

When I turn the breaker off, everything goes to 0. Other outlets on the same breaker work fine and give me 120V on my multi-meter.

Any ideas what the next trouble-shooting step would be?

Cheers,

Jesse
 
Sure sounds like a bad connection. First step is turn off the breaker, open the box containing the dead outlet, and visually look at the wiring. If everything looks good, do the same inspection of each box on the same breaker (WITH BREAKER OFF), because the power to that box is probably daisy-chained from another box.

It's rare that a wire will break in the middle. It's more likely that it will be loose in a wire connector or loose under a screw. Sometimes, people use the push connectors in outlets. These are not as dependable as screw connectors.

Worst case scenario is that previous repairs drove a nail or screw through the middle of a long wire and broke it. That's very unlikely but also very hard to debug.
 
Thanks for tip.. I'll take a look at other boxes on the breaker.
[automerge]1586284507[/automerge]
 

Reply to Faulty electrical socket in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

This is probably an easy question for an electrician but I was just curious about the theory. (I'm trying to figure out how things work!) I read...
Replies
4
Views
670
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
505
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
614
Our family room is part of an addition built a few years ago. We had an issue with nuisance tripping on an AFCI and the electrician came and...
Replies
2
Views
1K
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock