Discuss fcu from cooker circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

If you were designing for the appliances as a new install,you would be wise to follow the guides that recommend a dedicated circuit for the cooker,with a separate radial and perhaps off the local ring to the dishwasher

However, you are working with what is existing and you may consider the need to deviate from those recommendations that are in the guides,if you can still ensure safety

The use of a dedicated circuit for a cooker is a recomendation,follow that recomendation and you won't ever go far wrong,however,a recomendation does not mean"You must"

The first thought would be that the 6mm radial will most probably have already been de rated by the use of a 32 amp mcb at the supply end,depending on installation method,overload may not then be a problem (other than a nuisance factor if the mcb happened to trip occasionally if it was overloaded for a period of time)

Your opening suggestion,although not a standard arrangement appears to be a suitablee compromise,however,the cooker control could be changed to a straight DP isolator,doing that will reduce the possible unknown extra load from the existing cooker control integral socket

In short,if the posted information given is correct,it would not cause me nightmares if it was necessary to adapt such an arrangement to my own kitchen
 
19A for the hob/oven after diversity, plus max 9A for the dishwasher = 28A top whack whats wrong with that on a 32A 6mm?? Plus Westies right they probably never on together. I wouldn't worry about the Scam assessor the last one I had also had a bit of common sense.
 

Reply to fcu from cooker circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
819
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
744
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
576

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock