APE37

-
Reaction score
56
Hi guys. Just wondering, if you do a board change and client dont want spd or afdd would this need nothing on departures on cert? Looking at doing a board change for someone and use for assesment and as I have been off with hernia trying to get up to speed with things. Cheers
 
Is there a requirement for AFDDs on the installation?

Have you conducted a risk assessment regarding SPDs?
 
As above, are these required? If not then it's not something which doesn't meet BS7671.

Also, for it to be a departure it would have to afford equivalent safety. I'm not clear how simply omitting something could provide that.
 
Hi guys, it is a single dwelling house so I have offered spd but the client said no. So in my eyes it is not needed as the loss is low and it is a single dwelling. As for afdd I mentioned it and the associated cost and he flately refused. As they are only recommendations I was going to omit them and mention os risk assesment. but just wondering if they should be mentioned on the cert.
 
I know that manufacturers have to sell their products but they are making it look like you have to have this and we are getting a few posts on this stick to what the regs say.
 

Reply to Filling cert and including departures in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
956
Hi Folks , Just looking for a bit of advice as I'm looking to get back on the tools so please bare with me if this is a bit long winded. I'm a...
Replies
1
Views
640
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
361
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
933
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock