Discuss Fire Alarm- Earth Fault on Loop (XP95) in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
11
Hello,
Would welcome any advice-

We have an earth fault to a fire alarm loop, everything connected is XP95 and there are isolators in many bases and call points..

Is there a hints/tips way to find this, without having to gain access everywhere.
Would splitting the loop, powering the half that brings up 'Earth Fault' and disregarding the legs/devices that come up missing work?

I've asked Apollo for any hints/tips but they suggested we buy their test set. Which looks very good, but would hardly be used.

There is no water ingress or other faults at all.
Regards
 
split loop, using a logical process of elimination, keep splitting the bad part of the loop until you find the fault.
 
Break the loop down, isolate (disconnect) each section between the loop isolators until you clear the earth fault then test that section to confirm the earth fault and break that section down until you locate the fault
 

Reply to Fire Alarm- Earth Fault on Loop (XP95) in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
Replies
38
Views
4K
On this commercial building we are refurbishing it has the above fire alarm panel which I think is pretty much brand new, I'm not even sure it was...
Replies
6
Views
1K
Hi all Just a quick one. For a fire alarm loop addressable system. Fp200 1.5mm cpc 1.5mm To obtain R1+R2 would you treat the "loop" as a...
Replies
3
Views
2K
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
1
Views
345
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock