Both legs of one ring in a socket with both legs of another adding another 8 outlets in two rooms.

I'm adding a few new sockets and will be migrating the circuit to a new RCBO populated CU so was giving it a little more attention than usual, wouldn't normally do a fig8, when i found the two rooms significantly and consistently higher than the rest of the ring.

Obviously, said I, it needs correcting but other than it not being an approved circuit in BS7671 I can't think.....

...in writing this just thought, potentially 32A through a 20A double socket terminal.

Any other reasons?
 
You have hit the nail on the head.

1 week spot in the circuit that could become overloaded
Also, testing becomes rather difficult.
I.e the furthest part of the fig 8 could have a break in circuit that is not picked up by end to end testing at the board.
 
Both legs of one ring in a socket with both legs of another adding another 8 outlets in two rooms.

I'm adding a few new sockets and will be migrating the circuit to a new RCBO populated CU so was giving it a little more attention than usual, wouldn't normally do a fig8, when i found the two rooms significantly and consistently higher than the rest of the ring.

Obviously, said I, it needs correcting but other than it not being an approved circuit in BS7671 I can't think.....

...in writing this just thought, potentially 32A through a 20A double socket terminal.

Any other reasons?
Needs sorting Mate and quickly, any paperwork to cover this bodge up?
 
Needs sorting Mate and quickly, any paperwork to cover this bodge up?
What do you think Pete?

Purely coincidentally, a guy called pete did the work, good lad was pete, apparently.

I have opened it up and tested it, cert on the back of a smoke packet, will be moving it to a new CU later in the week.
 
Would have thought that with everything in one socket it would be easy to convert out/back to one ring?
It was very simple as it was a flying socket flung in a false ceiling. In fact I could pretty much walk through the whole circuit.

Wago box and wagos, done in ten mins, once happy with my inspection and testing.
 

Reply to Found a Figure 8 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
273
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465
Hi all, I just found this forum last night and figured I would post my issue since I can't find much out there with a similar situation. My job...
Replies
4
Views
411
Hello All done an EICR on a small office around 5 years old someone has added extra socket circuits from new to suit layout. they have added...
Replies
6
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock