I believe that regulation regards fine wire only.
It's upto the installer to be satisfied that the connection made is electrically sound and is suitable terminated.
If worried about crushing then use a torque screwdriver to manufacturers instructions
 
Regardless of which rules and regulations they fall under I'm talking about fine stranded flexible copper cable tightened with a screw terminal and without further 'treatment' , and with absolutely no ill effects.

Yes there are a lot of fine stranded cables terminated in screw terminals with no ill effects, but there are also a lot which have failed as a result of it.
I find it hard to believe that you have never encountered a flexible conductor which has been damaged by the tightening of a screw terminal.

any plug fitted by a manufacturer or supplier of appliances will have ferrules used on the flex, all of the equipment which we get new with a fitted flex has ferrules on the end ready for connection.
The standards which apply to equipment building, panel building etc all require ferrules.

Should we all just stick our heads in the sand and resist simple changes which make things just a little bit better?
 
In my opinion and experience fine stranded conductors when twisted tightly and even doubled can become much more rigid and tightening under a flat or rounded bottom terminal screw doesn't cause any significant damage.
 
I believe that regulation regards fine wire only.
It's upto the installer to be satisfied that the connection made is electrically sound and is suitable terminated.
If worried about crushing then use a torque screwdriver to manufacturers instructions

And flex is a fine wire conductor.

Applying the correct torque won't prevent the fine strands of flex from being damaged, that's why the regulations require that ends be suitably treated
 
Yes there are a lot of fine stranded cables terminated in screw terminals with no ill effects, but there are also a lot which have failed as a result of it.
I find it hard to believe that you have never encountered a flexible conductor which has been damaged by the tightening of a screw terminal.

any plug fitted by a manufacturer or supplier of appliances will have ferrules used on the flex, all of the equipment which we get new with a fitted flex has ferrules on the end ready for connection.
The standards which apply to equipment building, panel building etc all require ferrules.

Should we all just stick our heads in the sand and resist simple changes which make things just a little bit better?

No I'm all for changes which make things better Dave and actively try new products and methods but ferrules aren't always necessary and could be seen as another attempt to make something 'idiot proof'.
 
Take 1mm I double it up when terminating especially in db terminals mcb etc but take it out and it looks damaged regardless yet I'd say this is a fine wire that requires no specific treatment to it.
Most cases a doubled over flex is a better connection in my opinion.
I'm not convinced by that regulation perhaps connecting flex to copper say in a connection block then it may apply more id say.
 

Reply to Full rcbo boards???? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just wondering if any of you know which RCBOs might fit this old GET board? Cheers in advance!
Replies
4
Views
900
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
768
Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
943
Hi all, just a quick one to ask about an issue I'm having with my EV charger. I'll give a little background first but ultimately I want to know if...
Replies
11
Views
2K
Evening all. I did an EICR recently and then changed a consumer unit. As part of the EICR process I take off around 25% of all accessories to...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock