Whats peoples approach when dealing with the earth fly leads on RCBOs?
Got a board to fit next week and the bits arrived today. So been busy getting rid of packaging and putting bits together ready and checking its all arrived.
Hager say you can trim the fly lead and nuetrals down if needed as long as you use a suitable ferrule or termination. The supply neutrals arent so much an issue as they are quite thick.
The fly leads are so thin and flexible that i think id struggle to find a decent ferrule or crimped connector to go on the end to then go in the earth bar. Anybody got recommendations for ferrules?
Likewise how do you terminate them?
If i have space i will terminate them on their own in the earth bar. Otherwise i terminate with the corresponding cpc.
Keeping each circuits bits together.
Can be bit awkward with a ring final or 10mm circuit though. So in these instances i put them in the earth bar separately. Just got to be careful when tightening that you get a good grip as its easy for them to go down side of screw and be loose.
The new CU i am installing is only 7 RCBOS in a 10 way board so lots of space to make it look pretty.
 
If you cut them down then you will need to crimp them as instructed in both the Regs and the installation guide as you have mentioned, been a while since I done them and they may vary from manufacturer to manufacturer but probably a white or blue ferrule (bootlace) crimp will do...
I would have thought the majority of sparks now should have a ferrule kit as part of their tools, all fine stranded terminations require some form of crimping unless what you are terminating into is specifically designed for fine wire (e.g. - lever style connector). It amazes me tbh how many sparkies do not crimp up the cables when fitting a standard plug top.
If you have yet to build your tool collection up then just leave them as supplied and took them behind the raised dinrail mount if the board design allows you to.
 
I have more tools than i know what to do with. Some i dont even know what the tool is for other than it looked nice when i bought it.
I have quite arange of crimps and ferrules just none designed for such thin fly leads... I may have to invest in some for future jobs. This time i may just tuck them behind the din rail.
 
They can be a stretch on the budget, I have several crimpers myself which total quite a few pennies although I need a few crimpers most sparks would never need in their day to day jobs.
 
Hi Gavin - I bought one of these kits for a job that (in accord with Sod's law) promptly fell through. So I didn't use it much at first but, recently it's been pulling its weight. I've added some uninsulated ferrules now as well.
Ferrule Kit - German Colour Scheme - https://www.tlc-direct.co.uk/Products/DVDK2G.html

IMG_0799.JPG
 
I personally don't cut the functional earth leads just tie them up and loose any slack in the board, easy to do In a 3 phase db.

I've also never crimped terminals when fitting a standard 3 pin plug top as I don't quite see the need

This tends to be the problem in that people don't see an issue, plug tops tend to be a grub crew terminal with either a pointed, flattened or rounded base and often when fully tightened they have gaps to the side of the thread which the fine wire can be pushed into thus not getting a good solid contact, or with the pointed ones they can cut through the delicate stands as oppose to clamp them, on little loads like a table lamp etc this is really not going to be a concern but when you get to heavy loads especially those that are on for long duration then this can be a major factor to plugs overheating on the live or neutral pin.
Yes, twisting the strands can reduce the problem but it not a solution and as a professional should not be the solution, all products you buy where you can open the plug top will show that even the manufacturers have to follow the same rules here.

Don't get me wrong here, I was too one of those who thought nothing of wiring a plug up without crimping but when it was explained and shown then it was clear why the reg's exist on this and I have crimped them ever since, more than a decade later though when this was been highlighted in the trade I do struggle to understand why so many people still do not hold the correct attitude on this matter and/or why it is not been pushed and embedded in students minds at college level.
 
Can I ask a slightly different question.

Do you put the fly lead in the corresponding earth terminal?

Would it be a code on an Eicr if they did not correspond to the correct circuit/rcbo?

I recently saw an Eicr with a c2 because the neutrals and cpcs were not in the corresponding terminal on the earth/neutral bar
 
This tends to be the problem in that people don't see an issue, plug tops tend to be a grub crew terminal with either a pointed, flattened or rounded base and often when fully tightened they have gaps to the side of the thread which the fine wire can be pushed into thus not getting a good solid contact, or with the pointed ones they can cut through the delicate stands as oppose to clamp them, on little loads like a table lamp etc this is really not going to be a concern but when you get to heavy loads especially those that are on for long duration then this can be a major factor to plugs overheating on the live or neutral pin.
Yes, twisting the strands can reduce the problem but it not a solution and as a professional should not be the solution, all products you buy where you can open the plug top will show that even the manufacturers have to follow the same rules here.

Don't get me wrong here, I was too one of those who thought nothing of wiring a plug up without crimping but when it was explained and shown then it was clear why the reg's exist on this and I have crimped them ever since, more than a decade later though when this was been highlighted in the trade I do struggle to understand why so many people still do not hold the correct attitude on this matter and/or why it is not been pushed and embedded in students minds at college level.
Which Regulations for terminating a 13A plug top as a matter of interest.
 
Do you put the fly lead in the corresponding earth terminal?
Yes

Would it be a code on an Eicr if they did not correspond to the correct circuit/rcbo?
If securely attached and working then it's not dangerous so not C1. No possibility of danger if a fault occurred (that I can imagine), so not C2.
 
If i had a pound,for everytime someone asked "What you doing,there?"...it would be for crimping fine wire,when fitting plug tops.
It is something i have done for most of my working life-from the time me dads pal,gave me an old Gedore set of crimpers,and a handful of plain ferrules,from his P.O. supply bag.

What specific regulation covers this,in a domestic setting,i am not sure,but "correct and suitable termination of conductors..." covers this practice,amply.

No matter who or how,a plug top is fitted,one which has the conductors fitted with ferrules,looks more professional.

You can get a range of sizes,for about £12,put them in a little,sectioned Mustad fly-box (£3),the size of a phone,and stick it anywhere. Some Knipex multi-pliers come with a facility to crimp smaller ferrules,so these are your plug top pliers.

Time consuming,picky,pedantic? ...maybe. But certainly,professional. :cool:
 
i have to admit that with plug tops, i generally twist and double over. the ferrules with the plastic shields tend not to fit, and i can't be arsed buying the "plain" ones. i have been known to tin the ends though.
 
Hi - I take it from the general directive in 526.9.1 - your thoughts?
Yes that one where no definition is given for multiwire, fine wire or very fine wire. To me that covers all conductors beyond solid core does it not. Whatever it refers to the requirement is to fit suitable terminals or suitably treat the ends.
 
Hi - I take it from the general directive in 526.9.1 - your thoughts?
Yes that one where no definition is given for multiwire, fine wire or very fine wire. To me that covers all conductors beyond solid core does it not. Whatever it refers to the requirement is to fit suitable terminals or suitably treat the ends.
 
Still can't see any problem fitting 1.0 mm flex in a plug top without ferrules.
It's not like the terminals are massive nor the grub screw.
 
I use plain uninsulated ferrules in plugs and other accessories when building equipment in the workshop, but I don't lose any sleep if it's not convenient to do so out and about, as most plugs make a sound connection if the wire is suitably prepared. Some connectors like good quality IECs have conductor protection under the screw anyway and don't need ferrules at all. I first started ferruling in plugs after I saw sparks doing it in Germany in about 1989 when I was on a work experience exchange from school.

Re. RCBO FE flyleads I keep blue 0.75 and white 0.5mm² ferrules in the kit as standard.

Re. tinning ends of fine stranded, I don't like it at all. It makes things look neat but over time the solder cold-flows out from amongst the strands under the pressure of the screw. I've seen tinned ends in choc block go completely slack after a year or two of thermal cycling.
 
@westward10

Wilko has already pointed to the regulation which does express all fine-wire should be suitably crimped, I haven't the regs to hand but I am going by memory and previous discussion on this matter, the exception is if the connection device is designed to take fine-wire without it been dressed, plug tops are not designed to accept fine-wire undressed so the regulation applies that they would indeed need a uninsulated ferrule crimp.... insulated tend to have issues fitting in the plug top.

If you look at any BS standard goods that come with a terminated flex you should find it has been suitably crimped or has had special terminals fitted be it a drop, a plug top or the internal wiring of a product, you will not see them connected bare anymore into a standard screw terminal, the regulations are across the board, it is now our industry that is lacking in applying this standard and not the manufacturers as used to be 15yrs ago.
 
I can upload deta pendant if you like?
But I assure you the flex don't come crimped

Please do, is this a new pendant that hasn't been shortened or doesn't have specific terminations designed for fine-wire, if it is new and does not dress the fine-wire then it is probably in breach of their own BS regulations for such products... I am interested to see your upload as the last Deta I did was dressed cable ends but as they are uninsulated crimps you sometimes need to take them out to see the crimp.
 
@westward10
If you look at any BS standard goods that come with a terminated flex you should find it has been suitably crimped or has had special terminals fitted be it a drop, a plug top or the internal wiring of a product, you will not see them connected bare anymore into a standard screw terminal, the regulations are across the board, it is now our industry that is lacking in applying this standard and not the manufacturers as used to be 15yrs ago.

What about those MK plug tops, you would have to snip off crimped terminals :)

upload_2017-9-14_17-25-36.jpeg
 
@westward10

Wilko has already pointed to the regulation which does express all fine-wire should be suitably crimped, I haven't the regs to hand but I am going by memory and previous discussion on this matter, the exception is if the connection device is designed to take fine-wire without it been dressed, plug tops are not designed to accept fine-wire undressed so the regulation applies that they would indeed need a uninsulated ferrule crimp.... insulated tend to have issues fitting in the plug top.

If you look at any BS standard goods that come with a terminated flex you should find it has been suitably crimped or has had special terminals fitted be it a drop, a plug top or the internal wiring of a product, you will not see them connected bare anymore into a standard screw terminal, the regulations are across the board, it is now our industry that is lacking in applying this standard and not the manufacturers as used to be 15yrs ago.
Whilst I am not disagreeing the Regulation does not state they should be suitably crimped but "suitable terminals shall be used or the conductor ends shall be suitably treated", whatever that implies. Whether this applies to a plug top or fixed wiring, the latter I suspect.
 
This is the connection instructions from a rewirable plug top and it states nothing of fitting ferrules or the like.
20170914_174817.jpg
 
Please do, is this a new pendant that hasn't been shortened or doesn't have specific terminations designed for fine-wire, if it is new and does not dress the fine-wire then it is probably in breach of their own BS regulations for such products... I am interested to see your upload as the last Deta I did was dressed cable ends but as they are uninsulated crimps you sometimes need to take them out to see the crimp.
Back on site tomorrow so I will do
And I use deta all the time
 
Agree with Lucien - it is not good practice to tin the ends of stranded wire if they are being inserted into a screw terminal.

Ferrules in 13A plug-tops? Really?
 
IMG_3041.JPG
IMG_3043.JPG
IMG_3042.JPG
IMG_3040.JPG
IMG_3040.JPG
Please do, is this a new pendant that hasn't been shortened or doesn't have specific terminations designed for fine-wire, if it is new and does not dress the fine-wire then it is probably in breach of their own BS regulations for such products... I am interested to see your upload as the last Deta I did was dressed cable ends but as they are uninsulated crimps you sometimes need to take them out to see the crimp.
 
Yes that one where no definition is given for multiwire, fine wire or very fine wire. To me that covers all conductors beyond solid core does it not. Whatever it refers to the requirement is to fit suitable terminals or suitably treat the ends.

The terms are defined in other British standards and if you look at the data sheets for the cable it should tell you what type and class of conductor it is.
 
I will do some digging as to which standard cover the likes of deta and volex for pendants etc, but you can visually see the strands are not clamped correctly in those screw terminals, the only positive on it is the fact the current is so small compared to the ccc of that cable that even a poor termination with the fine-wire wouldn't give rise to an issue.
 
Agree with Lucien - it is not good practice to tin the ends of stranded wire if they are being inserted into a screw terminal.

Ferrules in 13A plug-tops? Really?

Not the ferrules with a plastic guide on them, non-insulated ferrules, like a bootlace without the plastic skirt, a lot of products now that come with plug tops that are not molded do use these crimps, the fact that screw terminals will by their nature push apart and splay the fine-wire even when they are twisted usually ending up with a poor termination is enough for me to say it should be done... look at post 40 by Ian - first pic and look how the manufacturers termination has splayed the cores and pushed them up the sides of the screw where they will be not clamped properly and often damaged by the sharp edges of the thread, the space at the side of the thread is clear in the pics and I cannot believe that the majority of manufacturers now crimp in this situation just because they want to as it adds time and money to make the product... I know that pendants are covered by the BS67 (1987) and this references many other regulations but as it's not the cheapest thing to buy it is hard to find any specific info, I believe it is like our regs in that there will be so many areas of compliance that these small things can be lost in the paperwork meaning some manufacturers may be in non-compliance, noted the two brands shown above are budget brands, they indeed may not be breaching any regulations at the end of the day but if is shown that the terminations at factory are not clamping the fine-wire correctly then it should be the case you do not need a regulation to alter how you terminate the product.
 
Last edited:
Since I've started to use ferrules more, I see more of them in use. I must've been ferrule blind o_O

The 10mm ferrules,are ideal for finishing my nieces plaits and pony-tails off,when she stays,as she kept coming back from school,with her bobbles missing...

Strange,but they seem shorter,every time she visits...
 

Reply to Functional earth fly leads and rcbos in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
961
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
4K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
Replies
17
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock