Discuss Funny business in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
645
Call out to a job,flat with Db protected by 30ma trip as main switch.
Rcd had tripped but not in clients flat,main intake area downstairs.
There I found a 30ma rcd which supplied Db in upstairs flat.
Apparently this as been tripping on a regular basis,& got worst,obviously no discrimination between rcd s,& so,a nuisance.
Did all the correct testing,& installation proved ok,rcd tripping times ok too.
Major concern is that it's a tt system,& there are other rcds in situ,controlling various other supplies.
At main intake a 100 ma time delay rcd is installed,& sometimes this trips,& causes havoc to all.
The flat seems to cause all this once tripped,tried explaining to client the ins & outs,but goes way over the head.
I think I gonna do a runner.
 
Why is it a TT system ? what testing have you done so far.
alot of the time RCD/RCBO's don't trip is that they stick as not tested quarterly
 
Sounds like a new design for the installation is needed, which could be an opportunity. As I read it, there must be a fault somewhere that's setting off the RCDs but it might be tougher than usual to find. If you do carry on with it - perhaps IR test circuits with external lights - I've had a couple of these go bad recently with the seasonal damp (and diy ... ).
 
Sounds like a new design for the installation is needed, which could be an opportunity. As I read it, there must be a fault somewhere that's setting off the RCDs but it might be tougher than usual to find. If you do carry on with it - perhaps IR test circuits with external lights - I've had a couple of these go bad recently with the seasonal damp (and diy ... ).
Cheers exactly what I think,its like your an electrician it's gotta be fixed now !!
This all happened late afternoon today,so most probably go back soon,or someone else's headache.
,cheers,happy new year.
 
I think exactly what Wilko has put above to also if there is a leakage to earth from each flat and landlords but not enough to trip 30mA but together trips 100mA how old is the installation.I would see if supply could be upgraded to PME etc if a earth is provided to the buildings nearby gives a good indication.
 

Reply to Funny business in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
789
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K
Hi all, I've installed a Tesla Gen 3 wall charger supplied by my client. For your information, the place that I installed is in a block of flat...
Replies
2
Views
1K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock