turned up to a residential property today to add a few double socket outlets only to find the fuse box in the area was being fed by a ring main on the main switch. Is this allowed ?
 
So there's a main CU supplying a socket ring main which in turn supplies another fuse box....is that correct? What is the fuse box supplying?
 
I'm confused, when he said 'fusebox' I imagined fuses. I really don't understand the layout....
 
well whats the ring thats feeds it fused at? it probably doesn't break any regs, but is liable to be overloaded and trip the MCB feeding the ring and DB.
is it an actual ring main , with sockets, or is it just a sub main wired up with 2 x 2.5mm conductors?
 
This is likely to work but not to be suitable for installation. The possibilities for overloading a cable are very real. However in normal use a socket circuit does not draw much power.
A ring final can only have a spur limited to 13A or a single double socket attached to it.
Effectively this is creating a very high current draw potential at a single point, which is not the intention for a ring final.
 
There was a thread about something similar a few months back. It's quite common to find garage boards fed by a 2.5mm RFC (I've come across a few myself), on installs carried out during the 70's, as this was seen as a cheaper alternative to 6mm on a 30 amp fuse.
Obviously, in this case, the RFC is straight off the main switch which is very naughty.
 
Last edited:
but this scenario appears that someone has tapped into a RFC to feed a sub-main. not good, IMO.
 
is it a good design - course not.
is it normal practice - nope
is it dangerous - not really

no matter what you add to the ring and however its wired its still limited to 32A.
if you replaced the remote CU with 3 spurs to feed those sockets and lights no-one would bat an eyelid.
the only downsides are uneven loading of the ring legs and no dicrimination between the mcbs.

must dash now , tels pulling a fast one in our chess game lol..........
 
is it a good design - course not.
is it normal practice - nope
is it dangerous - not really

no matter what you add to the ring and however its wired its still limited to 32A.
if you replaced the remote CU with 3 spurs to feed those sockets and lights no-one would bat an eyelid.
the only downsides are uneven loading of the ring legs and no dicrimination between the mcbs.

must dash now , tels pulling a fast one in our chess game lol..........

Sorry Biff but I HAVE to disagree. You could easily overload the RFC with such a configuration and it needs to be reviewed/improved. Anyone adding further sockets/breakers to the DB needs their bumps felt.
 
Sorry Biff but I HAVE to disagree. You could easily overload the RFC with such a configuration and it needs to be reviewed/improved. Anyone adding further sockets/breakers to the DB needs their bumps felt.

what happens when you overload a circuit protected by a mcb thats correctly rated for the job ?
it trips.......
 
If, as I read it, the RFC feeding the sub-board is taken directly from the CU main switch, then it IS dangerous, as there is no protection for that pair of T&E other than the main fuse. If, on the other hand, it's as I sometimes see it (An RFC from a 30 amp fuse feeding a sub-board), then as Biff says, it's protected and safe (however rubbish it might seem).
 
I have seen this happen before, when kitchen fitters have been around they do it so that the sockets etc within the area they are working comply with the regs as far as being protection via Rcbos.

Like others have already said it protected via 32amp so no overload to worry about
 
I would say that this spur off a RFC has now got out of control. You can't just keep adding to this spurred off CU, which may have been all well and good originally, just to supply a couple of sockets and a bit of lighting. Up to you, but i'd personally decline supplying any more sockets to this spurred CU, ...enough is enough!! lol!!
 
You could end up running the RFC at 32 amps constantly, a RFC is design with diversity in mine i.e. it will not run 32 amp all the time I have seen a RFC
installed to supply 3 heaters, T&E had over heated and gone brittle when I check current draw it was between 30 and 34 amps
 
I would have thought the major problem with this design is the size of the spur cable. If 2.5 T & E then this would almost certainly be overloaded. If the board was spurred off the RFC via an FCU with 13A fuse fitted then it is still a poor design but not dangerous. If the the spur is 4mm then not quite as bad but poor design due to loading in one section of RFC.
 
You could end up running the RFC at 32 amps constantly, a RFC is design with diversity in mine i.e. it will not run 32 amp all the time I have seen a RFC
installed to supply 3 heaters, T&E had over heated and gone brittle when I check current draw it was between 30 and 34 amps

cant believe this post hasnt been pulled........

2 x 2.5mm T&E legs combined is good for around 50A clipped direct so i dont see how
32A is going to trouble it in any way ?
and i guarantee if you were to test the cable to destruction it will probably carry double that before the insulation is toast.
absolutely no design issues arise when running a properly installed circuit to its max mcb rating , hence the cornerstone principle of In > or = to Ib.
diversity doesnt even come into it IMO.
 

Reply to Fusebox being fed by a ring main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
843
Hi all, I have been on a site repairing damage caused by travellers collecting copper for the last week. We have found and replaced cabling to get...
Replies
17
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
907
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock