Discuss Fused spur in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

C

craig141

Hi, I'm installing an outdoor light and am going to spur off a socket ring circuit, I was going to spur off a socket that was closest to where the installation is going up, but have realised that there is a spur coming off the socket outlet. Is it possible the have two spurs coming off the same socket outlet or not?
 
Short answer is no, I suggest you look at pg 362 in the regs, Reg 433.1, Ring and radial final circuit arrangements
You will need to have a Fused Connection Unit (spur) next to your ring socket to control the two (1 existing and 1 new) spurs you intend to put in.
 
agreed, the intention of the unfused spur off a ring was meant for one point only the reason being that a double socket could max pull about 26A with two 13A plugs pulling a full load (would never happen) and by adding to that your exceeding the current the cable can handle in worst case conditions
 

Reply to Fused spur in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
644
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
408
Hi I have a switched fuse spur where the cooker hood should plug in to… above the actual cooker. I was wondering if I could swap this out for a...
Replies
7
Views
580
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
679
Im running a ring main for all my sockets using 2.5 cable....as an after thought i was thinking to spur off one of my socket outlets and run up...
Replies
4
Views
575

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock