Discuss Gas installation pipe distance to CU in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
115
The best position for a CU is in a cupboard that has a vertical copper gas installation pipe that would be about 25-80mm from a metal CU. This pipe supplies a boiler. Not a gas service pipe, or gas meter, just a copper gas pipe, with no joints, near the CU.

1) Is this OK by current regs as CUs are metal, which reduces fire hazards?
2) If not, can the section of gas pipe near the CU be in some plastic trunking, making it conform?

Thanks
 
Never seen that one before.
I know it was 150mm when CUs were plastic, but they are now metal. So I wondered if the regs had taken that into account. Also does metal and RCDs make a difference. Things have moved on. I know between gas pipes and cables it is 25mm, which at times is difficult when around boiler pipes.
 
The standard is BS6891. Which of course we don't have to hand....

However, the subject is covered in the on site guide published by the IET. My copy of which is unfortunately located outwith the premises.
 
Never seen that one before.
Had some gas engineers replace a gas feed into a meter cupboard. (One of the wood butchers had put his circular saw through the existing lead pipe.)

I was sticking some down lights in the same room as the were ruminating about their route.

Basically the route was straight up, through the top of the cupboard, clipped to the wall and into the ceiling. However the old lead curved round a 6" thick joist so they decided to move the pipe to the side of the joist and straight down.

Only now when it entered the cupboard it ran 50mm alongside a 1970s switch fuse.

As they were leaving they said "oh, you'll have to move that over 100mm" quoting this 150mm rule.

Now if they hadn't just have assumed I may have tried to be accommodating but thier damn cheek got the better of me.

"Not happening" I said, so they're straight on the phone to their gaffer, who no doubt phoned my gaffer as he phoned me asking me to shift the damn thing.

Whose paying the bill I ask. "What bill, its only four screws" he says.

"Well.....

One, that switch may contain asbestos, so who's paying for that assessment?

Two, their is no slack on the cable so it will need extending but digging out so the junction box is away from the gas pipe.

Three, the sub main cannot be assumed to be more than 50mm deep in the wall (could actually see it at the top of the wall) and if I start altering it I have to bring it up to regs. So I have to either chase it out and cap it or RCD it.

But, Four, can't RCD it as there are RCDs in the board upstairs and I'd lose selectivity so it will need replacing with SWA.

So those "just four screws" are looking at £400 and two days work plus decorating/making good.

I can get started in the morning if you want"


Ten minutes the plumbers phone ring, swearing and sulking and the tools come out of the van....

Thought it best to have an early dart..?
 
So it's a gas installation reg. Anyone suggest a reason for the required clearance? There's nothing particularly vulnerable or fragile about a copper pipe, whatever is inside it.
 

Reply to Gas installation pipe distance to CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
610
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
When earthing gas and water service pipes do the 10mm earthing cables HAVE to come from the main earthing terminal (first tee) or can they come...
Replies
13
Views
4K
Hello there! Could anybody help me with this query please, I am not sure where to look up the information I need? As I understand it, cables...
Replies
3
Views
4K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock