Discuss Generator Dual Inlet Box in the UK Electrical Forum area at ElectriciansForums.net

SlimJim82

DIY
Reaction score
3
I have a professionally installed Generator Interlock on my 200amp load center in my 1-family residence here in the US. I have 10 gauge wire from the panel going about 10 feet to an outdoor generator inlet box with the big 30 amp RV kind of connection. This setup works well with a larger generator with the 30amp outlet.
What i'd like to do, is use a smaller Honda 2200watt generator but be able to plug it into the same system just to power up some light circuits in my house. Obviously, I will be limited on watts. The generator only has typical 15 amp outlets on it. So what I want to do is use the generator's 15 amp outlet and run a cord into a new generator inlet box with a different typical male 15 amp plug. My thinking is I'd mount a second box with the new style 15amp plug next to the 30 amp plug and wire it on the same circuit. This way, I could use either generator (not both at the same time) and utilize the panel's generator interlock.
My question here is, does this sound safe and code-compliant? Granted it's not typical, but rather than run extension cords up through a window, I thought it would be a cleaner look to distribute the power into my home. I'm also thinking that since it is a lesser-powered generator I don't really need to re-wire or add a whole new generator circuit. Link to a product I could use https://www.electricgeneratorsdirect.com/Reliance-Controls-PB15/p1084.html
Thank you in advance.
 
No, what you are suggesting is dangerous.
2 inlets connected to the same circuit means that when one is being powered by a generator, the other one is live with accessible pins you could touch.

have a lead made up with the correct 30A socket on one end and the correct 15A plug for the generator on the other end.
 

Reply to Generator Dual Inlet Box in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
537
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K
I have hooked up a 30 amp interlock switch to my main panel run off my generator. However, only my light switches work none of my plug-ins have...
Replies
10
Views
744
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
291
Legends, need some advice. I am a 12v automotive electrician, but have had a side project building a concession trailer for my dad. We have an...
Replies
6
Views
747

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock