D

Dave Osborn

I'm not a sparks.. but I'm hoping for a bit of advice for an animal rescue charity in kent..


Their generator fine on 110v but as soon as it's switched to 230v it trips even with no load... any ideas please?
 
You haven't given us much information so I can't give you much of an answer. What model generator? By 'fine' do you mean it generates 110V correctly or just that nothing trips? What is tripping - an MCB? Does 'no load' mean no plugs in the sockets?

If I guess that it is a type with a 110V outlet, a 230V outlet and a selector switch, and it does generate 110V OK, then likely causes are:
a) short in wiring to 230V socket
b) faulty selector switch not breaking parallel connection of windings before making series
c) short in generator windings bridging ends that are paralleled in 110 mode but 110V or 230V apart in 230 mode.

a) and b) probably commercially viable repair, c) maybe not.

But first, fill in the blanks...
 

Reply to Generator tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
346
Hi, Hope you’re keeping well. Currently have an issue onbaord with regards to one of generators tripping. The generator is capable of taking...
Replies
1
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
823
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock