I'm having a problem with the electric running to my shop. I have electric, but when my compressor or chop saw is running, the lights go extremely dim, and the saw is not running at full speed. The compressor is struggling when it is trying to build up. I've checked the voltage at the circuit breakers, and they all read 120V. If I run these components from an extension cord from the house, everything works normal. The wires running from the meter to the shop look fine, and nothing appears to be loose. Any advice would be much appreciated.

breaker box.jpg


electric at shop.jpg
 
You may be suffering from Voltage drop when loads are applied, get the Utility people to check, don't know how the US deal with this sort of thing. you can only report the problem, could be the cables feeding your shop are to small.
 
Last edited:
Pete999 - Base on your reply I checked the voltage at the circuit breaker (123V) and then had one of my kids turn the fan on to my portacooler. The volts dropped down to 75V. Everything was working a few weeks ago with no issues. What could cause a drop in voltage like this?
 
Just a thought if it is the voltage. Which it probably is from the description of the opening post. Would a voltage optimiser combat this problem.

Not sure how they work.

I know they increase the voltage to a property that has low incoming voltage, but would it be any good as a reactive measure of when the voltage suddenly drops?
 
Pete999 - Base on your reply I checked the voltage at the circuit breaker (123V) and then had one of my kids turn the fan on to my portacooler. The volts dropped down to 75V. Everything was working a few weeks ago with no issues. What could cause a drop in voltage like this?
Supply cable not sized correctly, any extra loading recently, new machines etc, could have been OK when the supply was fitted but people are well known for adding loads without consideration for the cables supplying the building.
 
Pete999 - Base on your reply I checked the voltage at the circuit breaker (123V) and then had one of my kids turn the fan on to my portacooler. The volts dropped down to 75V. Everything was working a few weeks ago with no issues. What could cause a drop in voltage like this?
That's a 39% drop in voltage. Is this a new setup or has it worked previously and this has just occurred.
 
That's a 39% drop in voltage. Is this a new setup or has it worked previously and this has just occurred.
It's an old setup. Literally nothing plugged into any of the outlets. Only thing running is some florescent lights. Took them out of the equation, and the voltage still drops when a load is applied. This just started happening a few weeks ago. I've not added anything electric to the shop. I checked the voltage drop with just the florescent lights turned on, and it dropped from 123V to 119V.
 

Reply to Good volts but low power output in the USA Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, So I purchased a Novopal 2000w/4000w(Peak) Pure Sine Wave Inverter DC 12V to 110V/120V. I purchased this so I can hook it up directly to...
Replies
5
Views
692
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
579
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
271
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
571
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
694

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

USA Electrical Advice

Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.

UK Electrical Forum

This is the main UK Electrical Forum at ElectriciansForums.net. Electrician State Laws for Electrics and Electricals may differ on a state-by-state basis. American questions and answers can be found in our UK electrical forum.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock