Ok. This is based on real fault finding.
Rcd tripping. Socket circuit was the cause. A nail had clipped the live core, the damp , very newly plastered wall was allowing a path to the metal back box which was connected to earth. Disconnect earth to back box and rcd would hold.
The nail was about 9 inches from the back box.