Hi guys, i'm not an electrician ,I'm a builder.

a month ago we had an electrician in first fixing, after he left some capping fell off and i put it back on with a nail. turns out i nicked the cable but it wasnt live until yesterday when he second fixed the outside light and powered on and left. I wasnt on site but later the customers got a shock from the wall several feet from the cable, the whole wall was live , because it was damp from the plastering i had done (like 3 weeks ago) and i nicked the cable. so its all my fault i am told.

Should this not have been picked up on the insulation resistance test?
And why did the electrics not trip? i mean if i put the nail into the cable today would it trip or would the whole wall be live? i got a severe telling off for putting customers lives at risk but builders sometimes damage hidden cables and it always trips and never in my life have i heard of a whole wall being live like this was.

Please post honest opinions. i need to know if its my fault.

thanks
James
 
Hi guys, i'm not an electrician ,I'm a builder.

a month ago we had an electrician in first fixing, after he left some capping fell off and i put it back on with a nail. turns out i nicked the cable but it wasnt live until yesterday when he second fixed the outside light and powered on and left. I wasnt on site but later the customers got a shock from the wall several feet from the cable, the whole wall was live , because it was damp from the plastering i had done (like 3 weeks ago) and i nicked the cable. so its all my fault i am told.

Should this not have been picked up on the insulation resistance test?
And why did the electrics not trip? i mean if i put the nail into the cable today would it trip or would the whole wall be live? i got a severe telling off for putting customers lives at risk but builders sometimes damage hidden cables and it always trips and never in my life have i heard of a whole wall being live like this was.

Please post honest opinions. i need to know if its my fault.

thanks
James
This Electrician that did the first fix, was he the same Electrician who di the 2nd fix and testing and eventually livening up the installation?
 
If the problem only shows with the light in question switched on the fault is between the switched live and earth and if said switch was off [which it shouldn't have been] when he tested it wouldn't have shown up. But regardless it should operate the RCD - unless the nail has severed the CPC and there's no continuity on it back to the CU.
 
New posts

Reply to Have a major problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
515
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
688
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
677
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock