Maybe lack of coffee etc ! Voltage also dropped to 140 for a bit . New ring . wired up correctly but indicated "reverse " . Could not be possible . Then tested other way and same thing ! Its a luxury apartment and only in there fitting longe plates. Building sparks arrived and fiddled in Consumer and it all came back to life. My remit did not allow me to open Consumer
 
My best guess as follows:

Dead tests all passed fine.
Someone then manages to connect L+N backwards at consumer unit. More likely in an RCBO hence earlier question.
Circuit is energised for live tests.
Plug in and Zs test or RCD test will upset tester as Live to Earth is 0v and N to Earth is 230v. Most makes will show a warning lamp, or not light one of two orange lamps.
While removing either N or Earth some testers will show half supply voltage, maybe that explains that bit.

What I haven't worked out yet is your comment "tested other way and same happened". Did you swap two test leads over? If so was it definitely L and N you swapped?
 
My best guess as follows:

Dead tests all passed fine.
Someone then manages to connect L+N backwards at consumer unit. More likely in an RCBO hence earlier question.
Circuit is energised for live tests.
Plug in and Zs test or RCD test will upset tester as Live to Earth is 0v and N to Earth is 230v. Most makes will show a warning lamp, or not light one of two orange lamps.
While removing either N or Earth some testers will show half supply voltage, maybe that explains that bit.

What I haven't worked out yet is your comment "tested other way and same happened". Did you swap two test leads over? If so was it definitely L and N you swapped?
THis would make sense. I was there only to fit some custom lounge plates . Was told not to touch CB etc by property manager as The client is still "buying" the property ! I swapped L & N and still got the initial error message
 

Reply to Head went funny.... Reverse polarity showed up and still after swapping cables ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey there, I don't normally post much on here but am always browsing through this forum as the topics are somewhat interesting. Anyway, as per...
Replies
38
Views
4K
MikeL1
M
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K
B
Hi..! I had 2 soladin 600 gbr models 1 of them was and is still working which is the first grid tie inverter i bought. i used it since january-...
Replies
2
Views
4K
bob2041
B

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock