Discuss Help wiring Honeywell DT2 thermostat in the Central Heating Systems area at ElectriciansForums.net

I'm not sure about this - could somebody confirm my thoughts here:

The old Honeywell thermostat needed a neutral as it has a small heater resistor to reduce the hysteresis of the bimetallic strip. Photo below of the connections. From that the grn/yel wire appears to be permanent live in, the brown wire switched live to the boiler, and blue neutral.

But the new Honeywell Home thermostat, from the OP's picture, is battery powered and acts effectively as just a switch, and doesn't require a neutral.

So I think the green/yellow should go to terminal A, and the brown to terminal B, and the neutral safely terminated and not connected to the new thermostat at all.

Karatekid - does the lid of your old thermostat have the same diagram in it as the pic below, or any other info about which terminal is which? I do believe what you have called the 'earth' wire is very likely to be mains live, so I don't recommend experimenting until we are more certain of exactly which wire is which.

Anyone?

PS If the above is correct, and you leave the wires as you first connected them, but put the grn/yel into C, I think the boiler will run when the thermostat is off, and go off when the thermostat is on!
 

Attachments

  • 77966707-8CF4-4AE1-83CF-0397311E92D0.jpeg
    89.2 KB · Views: 11
Last edited:
I'm not sure about this - could somebody confirm my thoughts here:

The old Honeywell thermostat needed a neutral as it has a small heater resistor to reduce the hysteresis of the bimetallic strip. Photo below of the connections. From that the grn/yel wire appears to be permanent live in, the brown wire switched live to the boiler, and blue neutral.

But the new Honeywell Home thermostat, from the OP's picture, is battery powered and acts effectively as just a switch, and doesn't require a neutral.

So I think the green/yellow should go to terminal A, and the brown to terminal B, and the neutral safely terminated and not connected to the new thermostat at all.

Karatekid - does the lid of your old thermostat have the same diagram in it as the pic below, or any other info about which terminal is which? I do believe what you have called the 'earth' wire is very likely to be mains live, so I don't recommend experimenting until we are more certain of exactly which wire is which.

Anyone?

PS If the above is correct, and you leave the wires as you first connected them, but put the grn/yel into C, I think the boiler will run when the thermostat is off, and go off when the thermostat is on!
Yes its exactly the same inside. The earth is connected to number 1 on thr old stat. Ignore the red tape, I put that on.16066551562301553595109920947786.jpg16066552059751398104757489997067.jpg
 
OK, thanks for that.
Well unless the original owner didn't wire it correctly, that indicates your grn/yellow wire is mains live (so keep the red tape on it - or make it brown!), and the brown is the switched feed to the boiler. Those are the only two you need to connect to your new thermostat. As per my post grn/yel to 'A', brown to 'B', insulate the blue and don't connect it.

It would be wise to check this hypothesis first. Do you have a multimeter to check volts on the 'earth' wire? Care needed obviously.

Given that the old thermostat connected grn/yel to brown to make the boiler work, I believe the above will work.
 
This is battery powered to the only live in is from the programmer.

i cannot get a copy of the install manual as the Honeywell site is not providing it.

Do you have a copy?

do you have a Y or S system.?

(the y system has a 3 way valve while the S system has two separate valves.)

do you have a wiring system box with all connections within it? It would be easier to check the wiring from there and do you have volt meter and happy with using it?
 
I'm not sure about this - could somebody confirm my thoughts here:

The old Honeywell thermostat needed a neutral as it has a small heater resistor to reduce the hysteresis of the bimetallic strip. Photo below of the connections. From that the grn/yel wire appears to be permanent live in, the brown wire switched live to the boiler, and blue neutral.

But the new Honeywell Home thermostat, from the OP's picture, is battery powered and acts effectively as just a switch, and doesn't require a neutral.

So I think the green/yellow should go to terminal A, and the brown to terminal B, and the neutral safely terminated and not connected to the new thermostat at all.

Karatekid - does the lid of your old thermostat have the same diagram in it as the pic below, or any other info about which terminal is which? I do believe what you have called the 'earth' wire is very likely to be mains live, so I don't recommend experimenting until we are more certain of exactly which wire is which.

Anyone?
16066625964994494675763482019667.jpg
PS If the above is correct, and you leave the wires as you first connected them, but put the grn/yel into C, I think the boiler will run when the thermostat is off, and go off when the thermostat is on!
It works!!!! Green/yellow into A and Brown into B with Blue blocked off thank you!!!
 

Reply to Help wiring Honeywell DT2 thermostat in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I would like to replace my ancient Honeywell mechanical thermostat with a Honeywell T3R PROGRAMMABLE THERMOSTAT I have three wires in the old...
Replies
1
Views
3K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
1K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
565
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
585

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock