Discuss Help with spurs from ring main in the UK Electrical Forum area at ElectriciansForums.net

That would also apply if the ring was just extended one side, which might be easier?

A further wacky but universally accepted solution - if the intent was to cover this all with a blanking plate, then you could get hold one of these rare animals...
1708203497601.png

and fit a fused spur so both sides are fused down.
 
To my mind, there’s nothing wrong with the initial diagram. It’s two spurs off two separate points of a rfc…. Just very close together.

Extending the ring is favourable, but may be impossible now if those are existing spurs, and cable route is now difficult.

Switch fuse on a double box is certainly doable with grid switch and fuse modules. Could have a switch and fuse for both spurs on a 4 gang grid…. If you wanted to. It’s not required.
 
Two general points about fusing down to spur from a ring. Not directed at OP who's trying to make the best of a bad situation.

I'd seek to avoid doing so unless prominently placed for lighting. I've attended a couple of 'faults' where unknown spurs were well hidden and took some finding, with the actual fault being the fuse.

There has been a couple of mentions of 'switched' fused spurs. This is something else I'd seek to avoid, unless a switch is required for functional purposes - again such as lighting. It's not something I've encountered, but there have been several threads on this forum where 'faults' turned out to be due to an fcu being switched off and the poster finally learning the purpose of an unknown switch.

I like to think beyond the 'here and now' and try to make life as simple as possible for those who come behind me. Too often I'm the guy who comes behind and wish that those who were there before me had made just a little more effort 😂
 
In my opinion, the arrangement in the OP is fine.

I'd also say that both spurs from one connection point is fine too. Think of a twin socket with another twin socket spurred from its terminals, it would only be expected to introduce 2 twin sockets worth of load onto the ring at that point. If two spurs were connected to the same point on the ring via a JB, the same expected load would be on the connectors.
 
Thanks for all your input guys. It seems to be that it’s down to personal preference on the best thing to do/if it’s appropriate. In my head I can’t see an issue on how I’ve connected as per the diagram posted.
 

Reply to Help with spurs from ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
752
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
903
Hi all, I’ve had some good advice here in the last week or so which has made me ask a few more questions. 1. Ring main uses the old Red and Black...
Replies
10
Views
2K
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock