If you do end to ends at these sockets with a higher Zs reading, and you don't get continuity, then this socket will more likely to be a spurred socket. Importance of doing dead tests in the correct order. Although understand what you were trying to achieve, pre CU change.

Edit, as suggested by the other chaps!
 
Theres 2 rings in the bungalow. One for the kitchen and one for the rest of the house Kitchen readings were r1 0.49 rN 0.49 r2 0.83. So even these figures seem a bit high then? MFT has been calibrated recently and checked it against my Cal card the other day.
 
Theres 2 rings in the bungalow. One for the kitchen and one for the rest of the house Kitchen readings were r1 0.49 rN 0.49 r2 0.83. So even these figures seem a bit high then? MFT has been calibrated recently and checked it against my Cal card the other day.
If you are measuring the rfc loop e2e and it's made from 2.5 /1.5 then these seem ok to me as 0.49x2.5/1.5 = 0.817, so practical reading of 0.83 gets a tick :)
This would indicate an rfc about 65m length end to end and added to your Ze 0.14 should give Zs of around 0.47 ish which is fine for 32A. Is that roughly the Zs you've measured?
 
If you are measuring the rfc loop e2e and it's made from 2.5 /1.5 then these seem ok to me as 0.49x2.5/1.5 = 0.817, so practical reading of 0.83 gets a tick :)
This would indicate an rfc about 65m length end to end and added to your Ze 0.14 should give Zs of around 0.47 ish which is fine for 32A. Is that roughly the Zs you've measured?
Yep, 0.46 was my highest value in the kitchen. My calcs work out for the other ring (apart Zs sockets) work out, but r1 r2 & rN values are high if you put them against cable resistance table in GN3. See post 12 for other values.
 
The socket with the highest reading had 2 x 2.5 T&E. Took L-L, N-N, E-E reading at the consumer unit. r1 + r2/4 + Ze = 0.82 Ze was measured at 0.14. The calculated Zs of 0.82 was very near what i was getting all around the ring. 2 sockets were a bit lower (0.45 & 0.55) and apart from the 2 that were high, the rest were virtually spot on. ( My end to end values were L=0.92 N=0.92 E=1.83)
Td to end is a bit higher than expected calculation of 1.55 this may be down to loose/bad connection or 1.0mm cpc(or in part of) that aside did you do a R1 +R2 dead test this will prove that these two sockets are spurs. Midwest posted a good point in post #21 put the ends together at the C.U. and do a ring test at the high reading socket will prove it. You posted that there was still two cables at the highest reading socket my feeling is that there is another socket/outlet from this you have not located maybe in loft just a thought. Let us know what you find out on Monday
 
Td to end is a bit higher than expected calculation of 1.55 this may be down to loose/bad connection or 1.0mm cpc(or in part of) that aside did you do a R1 +R2 dead test this will prove that these two sockets are spurs. Midwest posted a good point in post #21 put the ends together at the C.U. and do a ring test at the high reading socket will prove it. You posted that there was still two cables at the highest reading socket my feeling is that there is another socket/outlet from this you have not located maybe in loft just a thought. Let us know what you find out on Monday
I hope its not in the loft, its covered in insulation. Two layers, And there's hardly any space to move....:rage:
 

Reply to High Zs value with 2 sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock