As it's a bungalow, you'll probably be able to stand upright. It'll be just moving the odd upright piano, travel chest and rolls of old carpets.
 
Im still scratching my head a bit as to why my r1 rn r2 values on the offending ring are as high as they are. The circuit cant be over 120m, so why so high?? ultimately if the Zs ok then its not a problem. Unfortunately my brain doesnt work like that and i always what to know why things are what they are!! Bit OCD!
 
Im still scratching my head a bit as to why my r1 rn r2 values on the offending ring are as high as they are. The circuit cant be over 120m, so why so high?? ultimately if the Zs ok then its not a problem. Unfortunately my brain doesnt work like that and i always what to know why things are what they are!! Bit OCD!

Haha, you might get lucky and find 100m drum of 2.5 in the loft with the ends connected to make part of the ring main. Get digging!

On a serious note... are there any sheds or outbuilding you could have possibly missed where they have installed that as part of a ring main? I have seen that down before!
 
Haha, you might get lucky and find 100m drum of 2.5 in the loft with the ends connected to make part of the ring main. Get digging!

On a serious note... are there any sheds or outbuilding you could have possibly missed where they have installed that as part of a ring main? I have seen that down before!
I was just thinking that.... half a reel in the loft! No,nothing outside. The customer has asked me to put some outside sockets in for him. Better put them on their own circuit or the end to ends will be off the map!!
 
Mystery solved. Took a few socket covers off and found lots of loose/poor earth connections and loose live connections also. Sorted these out and got much better Zs values and lower end to end values at the board. I carried out end to end tests at the problem socket (as a few of you guys recommended) and got readings of 0.03 for r1 and rn.
 

Reply to High Zs value with 2 sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock