Discuss Holiday let Fire Alarm in the UK Electrical Forum area at ElectriciansForums.net

EddieB

-
Arms
Reaction score
27
Now there's a requirement for a Fire detection in all bedrooms as well as hallways Lounge and Kitchens can the detectors be wired from the existing lighting circuit or must it be a dedicated circuit, I know what's best practice but the logistics make it very expensive and impractical
 
I think most folks here would say wiring to an existing light circuit is a better plan as if it trips folks know sooner and usually do something about it rather than stumble in the dark, where as for some alarms the backup is only a modest time so if it trips it might stop squawking in a while and nobody knows the alarms are dead.

Other here will know a lot more about the alarm categories, but in Scotland the requirement for linked alarms in domestic and similar properties is met by radio units with a sealed 10-year batter.
 
A fire alarm system is a very different thing altogether.
To meet Scotland regs you need SMOKE alarms with HEAT alarm in kitchen.

Think there’s a requirement for them to be interlinked too?
 
A fire alarm system is a very different thing altogether.
To meet Scotland regs you need SMOKE alarms with HEAT alarm in kitchen.

Think there’s a requirement for them to be interlinked too?
Yes, interlink is required, so I'm thinking of using the light circuit in each room for the power requirement and a wifi link between detectors
 
OK shall we agree on the terminology wireless, so far you've been very pedantic about the terminology, any constructive suggestions?
NO, when it comes to advice on safety systems like this, even informal as this is. it is important to get things factual.
smoke alarms and smoke detectors are different things, as are heat detectors and heat alarms.
fire alarms and fire detection are different entirely and come under different regulations.

I don't think anyone is trying to be pedantic or show up a lack of knowledge, just that sometimes more information is required to give good advice,
 
NO, when it comes to advice on safety systems like this, even informal as this is. it is important to get things factual.
smoke alarms and smoke detectors are different things, as are heat detectors and heat alarms.
fire alarms and fire detection are different entirely and come under different regulations.

I don't think anyone is trying to be pedantic or show up a lack of knowledge, just that sometimes more information is required to give good advice,
Hi James I'd be very interested in how these systems differ
Heat Detector v Heat Alarms the difference being?
Smoke Alarms v Smoke detectors the difference here is?
Fire Alarms V Fire detection the same question applies
I ask this because I'm truly intrested in the differences, remember here that the original question pertained to the change in a holiday let regulations and it. seems as if we are creeping into commercial and industrial detection systems for example an ANSUL detector in a commercial kitchen (HEAT) and the Air sampling systems as in Airports and Volatile areas ( VESDA for example )
 
Here in bonnie Scotland, Aico 10 year li battery smokes and heats, radio interlinked...there is no simpler system.
No redecoration, no raggling (chasing)of walls and ceilings, plastering, painting...
Just stick 'em up, pair them, walk away...I have never had a call-back on Aico yet.
OK, it's a very fast installation, so not a lot of money to be made, but the clients love them once you have sold the concept...especially the quick in and out and no other trades to make good. An extra £200, against about 3 times that for making good for hard wired...and it leads to extra work from satisfied clients.
 
Hi James I'd be very interested in how these systems differ
Heat Detector v Heat Alarms the difference being?
Smoke Alarms v Smoke detectors the difference here is?
A smoke alarm makes noise, a smoke detector signals to something else. same applies to heat detectors / alarms.
Fire Alarms V Fire detection the same question applies A fire alarm is a system designed to detect fire and "sound an alarm" often with the intention of evacuating a building / alerting emergency responders. Fire detection is simply the act of detecting a fire, it may signal a fire alarm and often does. however sometimes it will signal a control system to say "all is ok" as a fire is expected and fire going out would create a danger.

I ask this because I'm truly intrested in the differences, remember here that the original question pertained to the change in a holiday let regulations and it. seems as if we are creeping into commercial and industrial detection systems. Some Residential lets may require a far more professional fire alarm system that includes detectors and sounders compared to others that may only require stand alone or interlinked smoke/heat alarms.
for example an ANSUL detector in a commercial kitchen (HEAT) and the Air sampling systems as in Airports and Volatile areas ( VESDA for example )
 
Here in bonnie Scotland, Aico 10 year li battery smokes and heats, radio interlinked...there is no simpler system.
No redecoration, no raggling (chasing)of walls and ceilings, plastering, painting...
Just stick 'em up, pair them, walk away...I have never had a call-back on Aico yet.
OK, it's a very fast installation, so not a lot of money to be made, but the clients love them once you have sold the concept...especially the quick in and out and no other trades to make good. An extra £200, against about 3 times that for making good for hard wired...and it leads to extra work from satisfied clients.
I like the sound of this believe me but I'm. not. sure if it's. BS 5839 Part 6 Grade D1 Category LD1 compliant if it is sign me up
Here in bonnie Scotland, Aico 10 year li battery smokes and heats, radio interlinked...there is no simpler system.
No redecoration, no raggling (chasing)of walls and ceilings, plastering, painting...
Just stick 'em up, pair them, walk away...I have never had a call-back on Aico yet.
OK, it's a very fast installation, so not a lot of money to be made, but the clients love them once you have sold the concept...especially the quick in and out and no other trades to make good. An extra £200, against about 3 times that for making good for hard wired...and it leads to extra work from satisfied clients.
 
Now there's a requirement for a Fire detection in all bedrooms as well as hallways Lounge and Kitchens can the detectors be wired from the existing lighting circuit or must it be a dedicated circuit, I know what's best practice but the logistics make it very expensive and impractical
In the USA all smoke detectors are required to have their own circuit and be wired together so if 1 goes off they all go off.
 
Here in bonnie Scotland, Aico 10 year li battery smokes and heats, radio interlinked...there is no simpler system.
No redecoration, no raggling (chasing)of walls and ceilings, plastering, painting...
Just stick 'em up, pair them, walk away...I have never had a call-back on Aico yet.
OK, it's a very fast installation, so not a lot of money to be made, but the clients love them once you have sold the concept...especially the quick in and out and no other trades to make good. An extra £200, against about 3 times that for making good for hard wired...and it leads to extra work from satisfied clients.
Do these still need a mains supply, if so it might not always be so simple.

If not then radio interlinked wont last anywhere near 10 years despite any claims otherwise. 1 year maybe, 10 years no way hosea.
 
In the USA all smoke detectors are required to have their own circuit and be wired together so if 1 goes off they all go off.

This is allowed in the UK but it is preferred to supply them from a regularly used lighting circuit. This way ensures that if the circuit trips it will be noticed quickly.

Also we are allowed to use radio linked alarms or have them wired together.
 
Do these still need a mains supply, if so it might not always be so simple.

If not then radio interlinked wont last anywhere near 10 years despite any claims otherwise. 1 year maybe, 10 years no way hosea.

Years ago I would have agreed on the battery issue.

Now the batteries and the alarm technology are much better, however I would not install something like Fire Angel (they had a product recall a few years ago as 10 year batteries lasted 1.5 years)

On the other side I install Aico battery interlinked alarms and have had almost no failures, the failure rate is less than 0.05% (we have installed lots), we tend to get the client to buy them direct from the wholesaler to keep our turnover down
 
Thanks James
I believe that the original question would have negated most of your need to display your knowledge on Fire Alarm systems, however thank you for your manufacturer recommendations
 
Years ago I would have agreed on the battery issue.

Now the batteries and the alarm technology are much better, however I would not install something like Fire Angel (they had a product recall a few years ago as 10 year batteries lasted 1.5 years)

On the other side I install Aico battery interlinked alarms and have had almost no failures, the failure rate is less than 0.05% (we have installed lots), we tend to get the client to buy them direct from the wholesaler to keep our turnover down
Hi, baldelectrician doesn't BS 5839 Part 6 Grade D1 Category LD1 compliant regs want mains powered units as opposed to all battery which falls into the BS 5839 Part 6 Grade F1 compliant regs?
 
I think you’re mixing me up with someone else, I made no manufactures recommendations.
only made a point about definitions
 
Ok… I’ll bite.

Oscar… are you suggesting that aico, with a 10 year battery, no mains power will not last 10 years because of the rf functionality?

I would estimate 50% of Scottish homes have at least one of these types of detector since the new legislation came in. Possibly more.



Are we certain OP is in Scotland, or was that just to explain something?
If they are, then all domestic properties are the same whether owned, rented or holiday accommodation… it’s one smoke on each hall/ landing…. Heat in kitchen and smoke in “a room that gets used the most” like a living room.
Extra detectors can be put in if required according to layout of house.

However, some of my English customers just over the border have indeed needed detectors in bedrooms for holiday lets.
 
If not then radio interlinked wont last anywhere near 10 years despite any claims otherwise. 1 year maybe, 10 years no way hosea.
Ah you have used FireAngel then?

I would say that if you were doing a rewire than putting in the mains powered Aico would be better as the alarm modules are cheaper, more so when it comes to the ~10 year replacement due to sensor age, etc. I would still use the light circuit for powering it though unless something complicated where it had to be separate.

Best thing to me about the Aico range is the remote test/silence button, saves folks trying to wave a towel at them, etc.
 
Last edited:
Ok… I’ll bite.

Oscar… are you suggesting that aico, with a 10 year battery, no mains power will not last 10 years because of the rf functionality?

I would estimate 50% of Scottish homes have at least one of these types of detector since the new legislation came in. Possibly more.



Are we certain OP is in Scotland, or was that just to explain something?
If they are, then all domestic properties are the same whether owned, rented or holiday accommodation… it’s one smoke on each hall/ landing…. Heat in kitchen and smoke in “a room that gets used the most” like a living room.
Extra detectors can be put in if required according to layout of house.

However, some of my English customers just over the border have indeed needed detectors in bedrooms for holiday lets.
WHAT!!! you coming over the Border ...... Hahahaha!!
 
Ok… I’ll bite.

Oscar… are you suggesting that aico, with a 10 year battery, no mains power will not last 10 years because of the rf functionality?

I would estimate 50% of Scottish homes have at least one of these types of detector since the new legislation came in. Possibly more.



Are we certain OP is in Scotland, or was that just to explain something?
If they are, then all domestic properties are the same whether owned, rented or holiday accommodation… it’s one smoke on each hall/ landing…. Heat in kitchen and smoke in “a room that gets used the most” like a living room.
Extra detectors can be put in if required according to layout of house.

However, some of my English customers just over the border have indeed needed detectors in bedrooms for holiday lets.
Basically yes. It might possibly last that long in a lab environment in perfect controlled conditions but out in the real world do you really think a tiny little battery will still be functioning and transmitting perfectly over radio waves a decade after it is installed. I've not fitted or even aware of the fire Angel problem but that sounds a more realistic outcome to be fair.
 
in a lab environment, they possibly last 12 to 13 years or more... outliving the 10 year lifespan of the detector.

Aico have had them on the ,market long enough now to have tested them in real world.


the only thing i can see that might reduce their lifespan is if they are ringing more than the recommended frequency for testing them... like if someone burns the dinner every night, every week.....
 
There have been some recent changes to the fire regs applicable to holiday cottages in England, according to the company that books the guests for my three, and they came into force about six weeks ago.
No changes to anything to do with fire/smoke detection, but the two that affect me are a need to replace the external door locks with a type that don't need a key to open (turnbuckle on the inside, rather than keyhole), and a requirement to provide automatic lighting of some kind in the event of a power failure. This can be done by plug in rechargeable torches that light automatically if they lose power, but since my cottages are single storey, I'll probably fit a non maintained downlight in each.
 
There have been some recent changes to the fire regs applicable to holiday cottages in England, according to the company that books the guests for my three, and they came into force about six weeks ago.
No changes to anything to do with fire/smoke detection, but the two that affect me are a need to replace the external door locks with a type that don't need a key to open (turnbuckle on the inside, rather than keyhole), and a requirement to provide automatic lighting of some kind in the event of a power failure. This can be done by plug in rechargeable torches that light automatically if they lose power, but since my cottages are single storey, I'll probably fit a non maintained downlight in each.
Just started on the first of 18 properties, updating smoke alarms to hardwired interlinked 10yr battery ones.
 
Basically yes. It might possibly last that long in a lab environment in perfect controlled conditions but out in the real world do you really think a tiny little battery will still be functioning and transmitting perfectly over radio waves a decade after it is installed. I've not fitted or even aware of the fire Angel problem but that sounds a more realistic outcome to be fair.

Don't forget it's not constantly transmitting though.
 
The Aico mains powered battery back up only maintains power for approx four months if the power is off, the ten years quoted is the life expectancy of the battery whilst being charged from the mains, NB this is the mains powered battery units.
 
My personal experience is that I have had the Aico 10 year battery powered alarms in my home for 8 years now and there's no suggestion of the battery failing in any of the units. I installed the same ones in my daughter's flat 6 years ago, no problem so far. I have installed quite a few over the last 3 years, so maybe too early to tell, but I have no doubt the technology will see these battery units last 10 years.
FYI, my system and the system in my daughter's flat were installed as both properties were rented out. This was before:
1. The recent regs for ALL homes to have them, and
2. The recent regs allowing for battery radio-interlinked units.
My approach previously was a hybrid one, whereby the first unit was a mains powered unit with 10 year battery and radio-link, and the others were purely battery powered radio-linked. While not strictly complying when fitted, the design and construction of the properties was such that hard-wiring would be very messy, very time-consuming, very expensive. Also, both properties had the usual smoke in the hall, heat in the kitchen and smoke in the main living area. These 3 detectors are less than 6m apart, so if one sounds you really hear it throughout, whether they are interlinked or not!
Nowadays, they comply anyway so not a problem, and I live in the previously rented property and my daughter lives in hers.
I just think that the simplicity of the non-disruptive 10 year battery radio-interlinked Aico alarms is a great system, and my clients over the last few years have been very happy too chose that option.
 
+1 for Aico
Though annoyingly, not all that long after I fitted the multi-sensor smoke plus a CO right next to each other ... they have come out with a combo multi-sensor smoke plus CO in one unit.
The radio modules do add considerably to the price, not far off doubling the cost/head.
If radio linked, all the heads copy the sound of the alarm that triggered - different sounds for CO and smoke. But this doesn't work for hardwired interlink. And yes, you can mix/match hard-wired and radio as I've had to do in both of our properties since getting new cables around would have been impractical - perhaps when they are between tenants I'll reconsider the upheaval needed.
 

Reply to Holiday let Fire Alarm in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm completely rewiring a 9 bed 3 storey HMO in Jan, The fire detection required is just some linked lithium detectors in the...
Replies
7
Views
748
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
359
I know this has been brought up before but as a QS for a housing association ,i have been asked my opinion on interpretation of the regulations...
Replies
11
Views
3K
Hi all, I'm helping my friend do up an old house he bought a couple months ago and obviously we need to have mains powered smoke detectors...
Replies
3
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock