Malcolm
-
- Reaction score
- 19
Hi I hope someone can help with this. I cannot contact Honeywell to help by phone (lines constantly busy) I emailed them on Monday and still heard nothing.
I replaced a Honeywell smartfit wired controller and programmer with a Sundial Y9420S RF pack3 wireless system.
I have found that the boiler is not switching off. I have checked the wiring and everything looks ok against the Sundial wiring diag apart from the switch live from the boiler which isn't shown. What I did find out on testing was when energizing the system the programmer was all ok, the boiler was off. when I switched the heating on the boiler came on ok, and if I then turned the heating off after a few seconds the boiler switched off ok. But if I left the boiler on for a time then it wouldn't switch off?
Can anyone please help on this.
Thanks
I replaced a Honeywell smartfit wired controller and programmer with a Sundial Y9420S RF pack3 wireless system.
I have found that the boiler is not switching off. I have checked the wiring and everything looks ok against the Sundial wiring diag apart from the switch live from the boiler which isn't shown. What I did find out on testing was when energizing the system the programmer was all ok, the boiler was off. when I switched the heating on the boiler came on ok, and if I then turned the heating off after a few seconds the boiler switched off ok. But if I left the boiler on for a time then it wouldn't switch off?