J

Jester

This is probably going to be a really silly question but I need to know just for my own peace of mind.
I have a hot tub, an intex inflatable job. The power cable goes into an rcd then into a normal plug which is plugged into a normal house socket, (well away from the water I might add.) When I changed the plug it has no earth wire just the brown and blue. The tub has come from a friend and it's the original cable. Is this right? It is all plugged in and up and running but I don't want to get in it if it's unsafe in any way.
I realise I probably sound like a complete noob, it's because I am! I just thought it should have the earth wire or is that what the rcd is for? My friend says his tub is the same.
Appreciate any help at all! Cheers folks.
 
It does indeed have the square within the square. Thanks for the advice. Does this mean it's safe to use?
it should be fine. double insulated appliances don't require earthing as there are no exposed metal parts. the RCD operates on an imbalance between L and N, so will work without any earth on the appliance.
 
Is it safe to use? depends has it been maintained and installed correctly? has it been subjected to any tests (ISITEE) In Service Inspection and testing of Electrical Equipment you might know it as Portable Appliance testing (PAT)
 

Reply to Hot tub question for the experts. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
641
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
Replies
7
Views
2K
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock