Discuss Hot tubs and PME or TT in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
27
Hi guys I have a question on installing an outside supply to a spa at home. I have a few questions regarding this one is the consumer unit has no spare ways have checked maximum demand and all seems okay for an additional 32 amp load. My plan was to get a garage style CU and take out out of the 6 amp lighting circuit breakers at the main board and replace with a 40amp breaker to feed the new CU containing the lighting circuit and swim spa circuits. I’m then planning on running a 6mm swa outside to a rotary isolator.

first question is does the new CU require surge protection? (I know this will have to be signed off by someone who is registered as I’m not registered)

Does the lighting circuit require an installation certificate as well? I’m presuming it will as I’m installing it in a new board.

and lastly (I know there is many debates about this) but what are your guys thoughts on TNCS supplies and earth electrodes? I’ve been told by the manufacturer they’ve never heard of any electrician ask about using an earth electrode?

thank you for your replies in advance
 
The EIC will cover the new board and consequently the lighting circuits connected from it although the EIC doesn't strictly encompass the circuits as such. The EIC covers the new board and new circuit but you need to test the existing circuits and enter the results on the schedule.
 
So the circuit feeding the new board and the new CU circuits will all need testing. What is the regs on if it requires surge protection? I was always under the impression that every new install needs to be up to the latest regs so if I was adding an additional socket that’s not RCD protected I’d have to fit the whole circuit on an RCD to comply.
 
Depends if the tub is going to be used in a lightning storm....

No circuit "requires" surge protection. You may fit one UNLESS the customer asks not to have one. So its not mandatory.
 
Have a read of this...
... the punchline is you don't need an SPD in "single dwelling units where the total value of the installation and equipment therein does not justify such protection".
I'd also comment that this is a sub-main, surges on the incoming supply have already done their damage, and direct lightning strikes on the sub-main's cable are probably unlikely.
 

Reply to Hot tubs and PME or TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
624
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
698
I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
Replies
5
Views
923
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
869
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
990

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock