Discuss How many 4mm T & E down a 25mm conduit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Can you get 2 4mm T & E cables down a 25mm conduit that only has a kick and a female bush one end and a 2 g socket including a bush the other end ?
should think so. 2 x 2.5mm will go in 20mm conduit, just.
 
but what if he's running T/E clipped direct at high level and protecting his drops with conduit?
 
The job is a school im tendering they propose to use a basket installation at high level with dado dropping most of the cables down to low level but cleaners sockets and a few other spurs etc are not on dado there is no capping in the spec only galv conduit is included. I was hoping to use one 25mm pipe instead of 2 x 20mm.
 
Can you get 2 4mm T & E cables down a 25mm conduit that only has a kick and a female bush one end and a 2 g socket including a bush the other end ?
I've been in that situation many a time. The solution is:
Leave approximately 200mm of the sheathing on 1 cable or enough to make entry to the point of termination with sheath around it.
Strip the sheath from the 200mm mark to approximately 200mm short of where the other end terminates.
Now you have 3 building wires with no plastic sheath making them bulkier. Legal if run in conduit.
Its sometimes easier to strip as you go.

Keep the whole sheathing on the second cable, the conduit is wide enough to accommodate the cables as per described. Most important that any cables exposed should be sheathed.
 
I've been in that situation many a time. The solution is:
Leave approximately 200mm of the sheathing on 1 cable or enough to make entry to the point of termination with sheath around it.
Strip the sheath from the 200mm mark to approximately 200mm short of where the other end terminates.
Now you have 3 building wires with no plastic sheath making them bulkier. Legal if run in conduit.
Its sometimes easier to strip as you go.

Keep the whole sheathing on the second cable, the conduit is wide enough to accommodate the cables as per described. Most important that any cables exposed should be sheathed.
I'm hoping he may have finished the school job by now :)
 

Reply to How many 4mm T & E down a 25mm conduit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
193
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
841
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
593
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
804

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock