Discuss How to calculate site load and availability for expansion? in the Electricians' Talk area at ElectriciansForums.net

Reaction score
1
I have been tasked with seeing if a site is capable of accommodating a large new installation.

I have done some working out but I'm not sure if I am going down the right lines, as this is not my area of expertise.

The site has a main fused switch disconnector on the main incoming supply, rated at 315amp. This then feeds a 300amp isolator, which provides power to the busbar chamber, where all the various DB's are fed from.

I have received usage data from the energy supplier. They have provided data from the previous 9 months. I have chosen the month with the highest usage. This was 13347.7kwh. This was over a 30 day period. I have then taken this value and divided it by the usage time over that 30 day period.

The site was running for 22 days out of 30, and for 10 hours a day. This gives me 220 hours running time. Therefore, I should have a kw value of 60.67kw (13346.7/220).

I have then used the 3 phase power formula, P=root3 x VL x I x Cos(theta), to find I. I have used a line voltage of 440 and an estimated power factor of 0.9.

I = 60.67kw/root3 x 440 x 0.9 = 88.45Amps.

Then comparing this 88amps to the total 300 amp supply. There appears to be large amounts of room for expansion and the site is no where near to overloading the supply.

Have I gone down the correct route here or am i completely wrong? is there a better way to do this?

Cheers
 
For an existing site the best thing to do is connect a data logger for a few weeks and get actual data so you can see what is going on.

Your maths is flawed as it assumes that the load is perfectly balanced and constant. In reality the load will not be balanced and will fluctuate throughout the day/night
 
As above a logger is the only way unless you can get hourly or less data from the energy supplier.
If it was an Office building it may have a fairly constant load, but if it's a factory or other production facility it could have wildly varying usage throughout the day and possibly a massive peak at start of day.
 
The only way i would do it is to use a logger as you will not only get sustained peak current but also power factor to help decide if some correction would increase capacity available. Get you skates on though as the period between Nov - Feb is typically (for my observations over time) the peak months. Measure all three phases as well as you may need a little jiggery to balance out the phases as you approach the limit of the supply. I have used VARservices in the past if you are struggling for a load survey
 
As well as the bare numbers, it might be worth trying to identify a few of the largest contributors to the total in case there are varying usage scenarios that you don't capture on the logger. For example, we had a site where provided only one studio was in use, it looked fine, but every now and then both would be at full load and it was pushing the supply fuses 10% over their rating.
 
I would go with the above. Hire a data logger to run for a week, or as @plugsandsparks suggests it might be easier and more reliable to get folks in how have a logger and know how to configure and save the data correctly from the start.

Also @Lucien Nunes point is very important: try and get some sort of a list/audit of what they think is in use and do a walk around with the head folks to confirm the list, and then try to get ideas of what sort of a current range they ought to be drawing, the typical usage pattern, and see if it matches the logger's results.

In some cases you will see less drawn then expected as often nameplates, etc, give max demands, in other cases you might find they have more loads in use than documented!
 
Lucien's point is a little raw for me as my last job was trying to work out why a plant that had been happy with 315a fuses, started to blow them. I went up and although could not work out why the load had gone up, it was not a fault just load and a lot more. After much head scratching we worked out some process heaters (which should only be used overnight) had started occassionaly coming on during a production run.... the reason ? - new chemical supplier delivering product to site at a lower temp than previous supplier and making heaters kick in. Solved by interlocking these heaters against process run.
 
For an existing site the best thing to do is connect a data logger for a few weeks and get actual data so you can see what is going on.

Your maths is flawed as it assumes that the load is perfectly balanced and constant. In reality the load will not be balanced and will fluctuate throughout the day/night
Cheers mate! Appreciate the help.
 

Reply to How to calculate site load and availability for expansion? in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
581
Maybe I've just been lucky, but I very rarely have an issue with customers paying, the vast majority have paid straight away or within a few days...
Replies
33
Views
2K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock