A

AReynolds

I am trying to select a suitable conductor size from Fig 4D1A of the BS 7671 Book, and am encountering a problem because the circuit does not conform to one Reference Method. The circuit conductors leave the distribution board in wall mounted steel trunking, then run through some steel conduit that passes through about 20cm of concrete wall, then finally through some PVC wall mounted trunking and two more 20cm concrete walls.

Technically, the points at which the cable pass through the three walls are Reference Method A, while the rest of the circuit would be considered Reference Method B. Given that the tabulated current using Reference Method A will be more stringent, do I have to consider the entire circuit as being Reference Method A for the purpose of determining the tabulated current, or can I consider it as being Reference Method B, given that 60cm of the 20m cable run are Reference Method A, with the remaining 18.2m being Reference Method B?
 
Hi AR - Unfortunately, I think the worst case should be used. But perhaps the route in conduit through the wall is method # 41/42 or 59/60 from Table 4A2 which are all B ?
 
Last edited:
I have had a look at Table 4A2, and while the wall does not contain thermal insulation, it does appear that the concrete blocks have a thermal conductivity of less than 10W/mk (most of the websites I have looked at quote values between 0.70-2 W/mk). I cant believe that I am going to have to return to the drawing board with the nasty Ci correction factor and the more stringent Reference Method A tabulated current, which in turn will increase the cable size from 4mm to 6mm- which is ridiculous for a 20m socket radial- all for 1.8m of wall!

Would it be acceptable to leave the circuit as Reference Method B if I tell the person drilling the conduit holes in the wall to double their diameter or something?
 
Treat it as Method B. If the wall forms part of a fire compartment it will require fire stopping so don't oversize the hole.
 
If the masonary has conductivity of 2W/mK this is a resistivity of 0.5 mK/W which means it qualifies as Number 57 in Table4A2 which is Ref method C, but please confirm :)
 

Reply to How to calculate the tabulated current (It) for circuits with multiple Reference Methods (A and B)? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
I have a customer who called me in to look at a small electrical fire. They are a welding and fabrication company and have several welders...
Replies
8
Views
2K
Hi there, I was just looking to find out what would be the most appropriate reference method to use. the distribution circuits leave the fuse...
Replies
2
Views
1K
S
Determine the minimum size of cpc for the circuit giving consideration to; Disconnection times Thermal Constraints? Here is what I have worked...
Replies
1
Views
1K
G
Using IEC reference method A and B for loose wires in conduit a I have derived the following max OCPD and in turn maximum current loading for...
Replies
21
Views
6K
Gardner
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock