Discuss how to detect easily damaged cable under floorboards in the UK Electrical Forum area at ElectriciansForums.net

nk1255

DIY
Reaction score
2
hello

theres a damaged cable under floor boards in either the living room, hallway or dining room.

the 'downstairs sockets' mcb type b in consumer unit trips as soon as i flick it back up, so the problem is in one of the rooms above.

how do i detect which cable under the floorboards it is without having to remove carpets and dining room tiles, as that's a big job and costly.

are there any qualified electricians on this forum that can help with how to identify the problem from the consumer unit?

i was told that you can check from the consumer unit ( from the mcb type b that has tripped) or from the ring main.
apparantly you can use a multimeter(?) to check which cable from the ring main (tripped mcb type b) has dropped voltage/amps.
also can check the cables in each socket which is affected with a multimeter.

how can a megger ( insulation meter) be used to check which cable is damaged?

thanks

 
To be honest you'd be better employing a good electrician with the right test gear , that way the fault could be identified and fixed pretty quickly and you then know the circuit is safe for continued use.
Many small jobs can be done safely by a competent DIYer but this needs knowledge and experience of fault finding.
 
You pick up the multimeter, turn it to the off setting and put it down. Next you pick up your phone and call an electrician ?

Seriously though... fault findings an art (not a recognised one) and if you've never used a multimeter or megger before let alone done any fault finding, you'll struggle and we would be backwards and forwards forever trying to explain to you how to use it, what the readings mean etc etc
 
hello

theres a damaged cable under floor boards in either the living room, hallway or dining room.

the 'downstairs sockets' mcb type b in consumer unit trips as soon as i flick it back up, so the problem is in one of the rooms above.

how do i detect which cable under the floorboards it is without having to remove carpets and dining room tiles, as that's a big job and costly.

are there any qualified electricians on this forum that can help with how to identify the problem from the consumer unit?

i was told that you can check from the consumer unit ( from the mcb type b that has tripped) or from the ring main.
apparantly you can use a multimeter(?) to check which cable from the ring main (tripped mcb type b) has dropped voltage/amps.
also can check the cables in each socket which is affected with a multimeter.

how can a megger ( insulation meter) be used to check which cable is damaged?

thanks

Where are you situated?
 
thanks everyone

im not going to find the fault myself! im not an electrician!

i want to know how to identify the problem step by step
step 1 what to check
step 2 what to check
etc
also what equipment is needed

then i can call an electrician to check
if i know what checks are to be done, then ill know if the electrician is ripping me off or not!
 
thanks everyone

im not going to find the fault myself! im not an electrician!

i want to know how to identify the problem step by step
step 1 what to check
step 2 what to check
etc
also what equipment is needed

then i can call an electrician to check
if i know what checks are to be done, then ill know if the electrician is ripping me off or not!
I dont ask my Dentist for step by step info on how to do his job or what equipment is needed.
 
thanks everyone

im not going to find the fault myself! im not an electrician!

i want to know how to identify the problem step by step
step 1 what to check
step 2 what to check
etc
also what equipment is needed

then i can call an electrician to check
if i know what checks are to be done, then ill know if the electrician is ripping me off or not!
Rather than all this just get some recommendations from family. friends or colleagues , we're not all rip off merchants !
 
thanks everyone

im not going to find the fault myself! im not an electrician!

i want to know how to identify the problem step by step
step 1 what to check
step 2 what to check
etc
also what equipment is needed

then i can call an electrician to check
if i know what checks are to be done, then ill know if the electrician is ripping me off or not!
He could do all the necessary checks and still Rip you off. If, as you say its a persistent trip then at least he/she should get good consistent readings. From then on its a bit of common sense and a small dose of the "force".

If he/she can detect the fault from the CU, then easiest to break the cct roughly half way and follow your nose. Sometimes you can be lucky and find it within minutes as the giveaway is a newly painted wall or sometimes you can be there a couple of days as i found out in a commercial office a few years ago.
 
Whether you know what he's going to do or not, if he's gonna rip you off he can just make up some complicated sounding problem and do a load of unnecessary work and charge you a bomb for it.

Sounds to me like you're wanting to try and tackle it yourself. No offence but the old 'i'm going to get an electrician i just want to know exactly step by step how to do it first so i don't get ripped off' is the oldest trick in the book.
 
As already mentioned, start by ruling out the accessible stuff by checking all of the socket outlets fed from that MCB.

Obviously you have to make absolutely sure the power is off to the sockets being checked, simplest DIY option is a socket tester (having proved it works in a working socket, e.g. upstairs) on each and every downstairs socket before you open it up. Never assume they are all on the same supply, someone might just have done something really dumb... Or if you can (daytime, enough light, etc) just put off the main CU switch.

If you can rule out a fault at the socket backs (e.g. cable cut on back box as no grommet, etc) then it could well be a cable fault under the floor, or some hidden junction box, but identifying that location is much harder. Generally UK sockets tend to be wired in a "ring final circuit" (though they might be radial) and if you have a suitable insulation tester you can disconnect the CU end, split the ring at a known location such as furthest socket, and then see which of the halves has the fault. Then proceed to divide and conquer until you have found the faulty link.

However, messing around with the CU is really not to be suggested as a DIY activity as there is a real and serious risk of if going badly wrong. Also you need to be aware that a multimeter is not very good at fining cable faults as they only test at a couple of volts max, and if you ever do plan on using a multimeter on mains cable always make sure it is CAT-III or CAT-IV rated! Some cheap or old meters have little protection against a high energy fault and sadly folk have died from the resulting explosion/burns before, so it is not something to ignore.

Typically an electrician would have a Multi Function Tester (MFT) that includes insulation resistance at 250V or 500V, though some prefer a stand alone IR tester (often known as "megger" in the same way we refer to hoovering the floor, first big brand name). Not only are they ideal for cable fault testing, they are also designed to be safe if accidentally testing a live circuit.

Which we all know should not happen as we all follow safe isolation procedures, don't we? But sometimes in life sh*t happens and you really don't want your day to get any worse due to inadequate instrument safety.
 
All plugs from the sockets in affected room are out of socket, i tried to push mcb up thats tripped, and the mcb stayed up but mains socket rcd tripped. So cant be socket problem!
Maybe cable in the mcb??
Maybe the mcb??
 
All plugs from the sockets in affected room are out of socket, i tried to push mcb up thats tripped, and the mcb stayed up but mains socket rcd tripped. So cant be socket problem!
Maybe cable in the mcb??
Maybe the mcb??
Haven't read the whole thread but you said "room " ?

You.need to get everything unplugged and switched off connected to a tripping rcd

That's your starting point, that or isolating circuits to see where the problem is
 
I would definitely get an electrician in to so some testing. It's not good to repeatedly close a circuit breaker on a fault.
 
As already mentioned, start by ruling out the accessible stuff by checking all of the socket outlets fed from that MCB.

Obviously you have to make absolutely sure the power is off to the sockets being checked, simplest DIY option is a socket tester (having proved it works in a working socket, e.g. upstairs) on each and every downstairs socket before you open it up. Never assume they are all on the same supply, someone might just have done something really dumb... Or if you can (daytime, enough light, etc) just put off the main CU switch.

If you can rule out a fault at the socket backs (e.g. cable cut on back box as no grommet, etc) then it could well be a cable fault under the floor, or some hidden junction box, but identifying that location is much harder. Generally UK sockets tend to be wired in a "ring final circuit" (though they might be radial) and if you have a suitable insulation tester you can disconnect the CU end, split the ring at a known location such as furthest socket, and then see which of the halves has the fault. Then proceed to divide and conquer until you have found the faulty link.

However, messing around with the CU is really not to be suggested as a DIY activity as there is a real and serious risk of if going badly wrong. Also you need to be aware that a multimeter is not very good at fining cable faults as they only test at a couple of volts max, and if you ever do plan on using a multimeter on mains cable always make sure it is CAT-III or CAT-IV rated! Some cheap or old meters have little protection against a high energy fault and sadly folk have died from the resulting explosion/burns before, so it is not something to ignore.

Typically an electrician would have a Multi Function Tester (MFT) that includes insulation resistance at 250V or 500V, though some prefer a stand alone IR tester (often known as "megger" in the same way we refer to hoovering the floor, first big brand name). Not only are they ideal for cable fault testing, they are also designed to be safe if accidentally testing a live circuit.

Which we all know should not happen as we all follow safe isolation procedures, don't we? But sometimes in life sh*t happens and you really don't want your day to get any worse due to inadequate instrument safety.
Thank you for your detailed explanation. I have called a few electricians to come and check. Ill make sure they are qualified and have safe meters as per your info. Are you in london? If so you could have come!!
 
Can someone please recommend a reasonably priced electrician that can find the fault and fix near wembley.

First instance id rather get recommendations from here

Second google search

Thank you
 
I think reasonably priced would be subjective as anybody visiting your property would have to pay nearly £30 if they don't have a nearly new van. That doesn't include parking nor fuel lol. Plus what you are looking at is a call out charge which usually includes first hour and then an hourly rate to diagnose and find the fault. Repair the fault and issue any certs if applicable.
I don't know what your locals charge but down here in sunny/rainy east kent im £75 plus vat for the call out and £45 per hour after that. I would be adding the above London charges onto any customers bill though if I lived and worked up there.
Anyway Delroy is local and has a great reputation and has already been recommended.
 
I know a lad who lived near Queens Park which isn't too far from Wembley but he mainly does shop fit outs and would be looking at £150 call-out

Delroy is probably your best bet as this kind of domestic house 'fault diagnostics' is right up his street

 
I know a lad who lived near Queens Park which isn't too far from Wembley but he mainly does shop fit outs and would be looking at £150 call-out

Delroy is probably your best bet as this kind of domestic house 'fault diagnostics' is right up his street

And if you're lucky and the original installation is bad enough, you might make it onto YouTube and get lots of views which seems to be the most sought after currency these days!
 
And if you're lucky and the original installation is bad enough, you might make it onto YouTube and get lots of views which seems to be the most sought after currency these days!
yep, goood job I exchanged my bitcoins while the price wasup., once it's bottomed, i'll then buy cheap. who wants to buy some 2nd hand youtube videos?
 
yep, goood job I exchanged my bitcoins while the price wasup., once it's bottomed, i'll then buy cheap. who wants to buy some 2nd hand youtube videos?

I wouldn't take the mick! People are buying "memes" these days just to say they own them so I wouldn't put it past anyone to sell a YouTube video. Ridiculous. Some people have too much money!
 
May be a better idea to get a locksmith to cut the padlock off your wallet to start with
Then a optician to check your vision so you can see the right way forward

Think if you called me I would be on my guard from the start of dealing with you.

Good luck
 
thanks everyone

im not going to find the fault myself! im not an electrician!

i want to know how to identify the problem step by step
step 1 what to check
step 2 what to check
etc
also what equipment is needed

then i can call an electrician to check
if i know what checks are to be done, then ill know if the electrician is ripping me off or not!
You can also buy a special seat that attaches to the sparkys shoulder so you can sit and make sure he is not time wasting
 

Reply to how to detect easily damaged cable under floorboards in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
793
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
879
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
324
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock