Discuss how to upgrade the earthing conductor? in the Industrial Electricians' Talk area at ElectriciansForums.net

T

theugly

hi all, just a silly question because i never replaced an earthing conductor before,

just finished an inspection. the earthing conductoris only about 6mm. i am thinking to upgrade it to 16mm. the end of the conductor is taped in the supplier's thick conductor. I think it is a TN-C-S system, the outside metal of the trunk is for neutral and earth. i untaped it and found the end of the earhting is buried in some dark color painting, can i forced the earthing out and replace it straightaway?

thanks a lot,
 
Last edited by a moderator:
Hi pal, not sure I would not want to be taking it off the incoming supply conductor, (think the term is "sweated on"). Have seen the conductor taken from the incoming supply into an Earth block and then 16mm main earth to board/10mm bonding to services etc.

Regards WA
 
I think you are talking about a TN-S system there mate.

Your probably looking at the swa from the incoming supply which is normally used as an earth for a TN-S system.
Did you say you have just done an inspection ?

Sav
 
Hi mate
What size are the tails
If its TN-C-S then the earthing conductor has to be 16mm if carrying out alterations and additios

but you say the existing earthing conductor is connected to the suppliers conductor

If you are unsure mate what system it is or what to do then my best advice would be to contact the DNO to ask what type of earthing system it is
and if you are thinking of replacing this maybe you could ask the dno to upgrade as you shouldnt be messing with the DNOs cut out fuse or equipment they will fit a isolator and upgrade existing tails from cutout to meter and then to main 100A isolator switch and they will fit a earthing conductor to there equipment either by pme or tns

others more experienced may advise you better

what size are the Main protective bonding conductors to the water and gas

If your only carrying out a PIR then you only are inspecting the existing installation and should record observations and code as appropriate any code 1s need urgent attention or immediatly isolate the defective part code 2s require improvement
 
from all the replies do you all mean that 6mm is ok from supply to earthing block, as long as from earthing block to consumer unit is16mm?
 
That will be a tn-s system and is the suppliers earth to met, so providing you have a ze lower than 0.8 ohms and the consumers earth from the met to the consumer unit is of an adequate size its of no concern to your pir. If on the other hand the small wire is coming straight off the sheath into the consumer unit i usually reterminate into an external met and take a 16mm into the cu it will then satisfy the cert as the consumers main earthing conductor is of the right size. you should neva mess with there incoming cable, if you take a ze reading and it doesnt satisfy you contact the supplier to upgrade hope this may help.
 
on a tnc-s earth is taken from the neutral conductor at the supply cut out, u may somtimes come across and installation where it has a wire from the sheath and the neutral to the met this would be recorded as a tnc-s and is where the sheath of the cable has broken down over the years and the resistance to earth has become to high so the supplier has upgraded the system to tnc-s and left the sheath earth terminated.
 
calm down guys, let me explain before you get further, i certainly know the difference between the two systems, but when you are on site, it is difficult to tell the difference between them, i know you guys are very experienced, but from on site guide i dont think it is very obvious and enough to make everyone can identify them immediately, so why not be more patient and more constructive?
 
calm down guys, let me explain before you get further, i certainly know the difference between the two systems, but when you are on site, it is difficult to tell the difference between them, i know you guys are very experienced, but from on site guide i dont think it is very obvious and enough to make everyone can identify them immediately, so why not be more patient and more constructive?

I like to think I am helpful here but it's one thing asking about the interpretation of a certain regulation and another thing asking worryingly basic questions AFTER an inspection.
 
If you haven't seen many of them then yes it may be a bit tricky, but for somebody who is experienced enough to do a periodic inspection, you should be able to do it in your sleep.

The purpose of a PIR is to determine the safety of an installation.

If you can't identity the earthing system, how can you tell that the Ze is low enough? This is a major safety issue.

I'm sorry mate but if you are indeed doing a PIR you may find yourself on more sticky wickets in the future.
 
Last edited by a moderator:
You could always have a lengthy phone call with the supplier and ask them what the earthing arrangement is, they should be able to give you the information you require, after being passed around about.

Also, never remove the tape or sleeving off the incoming supply unless you want to be prosecuted for tampering with the suppliers equipment!
 
Like iq said pir require an above knowledge of Bs7671, i served about 6 years before completing a pir on my own and the amount of people iv seen coding no rcd protection etc as code 1 !!! point is its in in depth test which requires a lot of on-site knowledge and the regs extremley well, sounds like u may of been thrown in the deep end iv had the same with employers in the past.
 

Reply to how to upgrade the earthing conductor? in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K
I've come to a decision, I just cant do work anymore that involves mad stuff, for example today - 2 bed flat that's had fire damage, someone has...
Replies
4
Views
828
Just a bit of a muse at the moment, work won't happen for a while, though I do already have the ducting. We have (what's left of - it was rotten...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock